I see that this is the peak load for a single space which is a core space. Does this space have any exterior walls, and is there a 2nd floor above this space. If its an interior area the outside weather conditions shouldn't have any effect on the cooling load for this space.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Travis Rhodes
Sent: Monday, May 02, 2011 2:40 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Odd peak cooling day
I don't know where I've gone wrong, but my peak cooling day is happening in December. The output is saying that there is a huge internal heat load from occupants on that day. As far as I can tell the occupant schedule is correct. Any insight into this is appreciated.
[cid:image001.jpg at 01CC08D8.9B766ED0]