[Equest-users] Baseline HVAC Type - Table G3.1.1 A&B (90.1-2007)
Peter Hillermann
peterh at westallarchitects.com
Mon Mar 28 12:39:45 PDT 2011
Jeff\Jeremy,
I looked at this question again last week and I have come to this conclusion
with our engineer.
When separating a building the difference between your thermal zones is what
is important. Like it says in the exception I think that the model is
separating 2 spaces that are totally independent of one another in thermal
function. IE as it says in the exceptions like an aquatic room with swimming
pool, where humidity and temperature would be completely different to say
offices right next door. The other exception talks about laboratories which
again would have to run on a totally different system.
These exceptions as Jeremy pointed out earlier would be very difficult to do
and fairly rare unless you are doing aquatic centers, factories,
laboratories, or other uses that require total system separation.
This is an interpretation and could be disproven especially by the person
that wrote ASHRAE with those exceptions, but for now that's how I read it.
Thanks,
PETER HILLERMANN
peterh at westallarchitects.com
westall
architects
3404 pierce drive
chamblee, georgia 30341
o 770.458.4113
f 770.458.5352
c 678.898.2936
westallarchitects.com
Description: e-signatureDescription: USGBC-Logo
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Peter
Hillermann
Sent: Tuesday, January 04, 2011 3:58 PM
To: 'Jeremy Poling'; 'Patrick J. O'Leary, Jr.'
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline HVAC Type - Table G3.1.1 A&B
(90.1-2007)
Jeremy,
Thank you for the advice. I agree with your assessment of whole building. I
did enjoy reading the interpretation section you suggested below. I think we
are all guilty of trying to work the code into our projects instead of
working our projects to meet code. Hehehehe.
Thanks,
PETER HILLERMANN
peterh at westallarchitects.com
westall
architects
3404 pierce drive
chamblee, georgia 30341
o 770.458.4113
f 770.458.5352
c 678.898.2936
westallarchitects.com
Description: e-signatureDescription: USGBC-Logo
From: Jeremy Poling [mailto:Jeremy.Poling at transwestern.net]
Sent: Tuesday, January 04, 2011 9:16 AM
To: Patrick J. O'Leary, Jr.; Peter Hillermann
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Baseline HVAC Type - Table G3.1.1 A&B
(90.1-2007)
I would also recommend checking the standards interpretations on ASHRAE's
website (http://www.ashrae.org/technology/page/121) since there are a few
that apply to those exceptions. The exceptions haven't changed between 2004
and 2007 so look at both for official interpretations of when to use those
exceptions.
In applying those exceptions, the baseline system from Table G3.1.1 must
still be used for the predominant condition, held by ASHRAE and the
USGBC/GBCI to mean the portion of the building with the larger square
footage (i.e. the office portion of a warehouse is not the predominant
condition). So even if one of the exceptions applied for your building, you
would still have to model at least a portion of the building with the
standard baseline from Table G3.1.1. (Peter - that is what the reviewers did
not say, probably to stay clear of the GBCI's rule about not offering design
advice).
Jeffrey - Table G3.1.1 is intended to apply to entire buildings, so unless
the two wings are completely separate with no shared party walls, systems,
foundations, etc. it will probably be difficult to get the reviewers to
accept using a different baseline for both of the wings. If one of the
exceptions does apply, it may be useful on one of the wings, but the
submittal should include a detailed explanation of why the exception applies
so the reviewers can understand the circumstances better - they tend to view
the exceptions as being more or less rare.
Jeremy R. Poling, PE, LEED AP+BDC
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Patrick J.
O'Leary, Jr.
Sent: Tuesday, January 04, 2011 6:11 AM
To: Peter Hillermann
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline HVAC Type - Table G3.1.1 A&B
(90.1-2007)
see appendix g, section g3.1.1, exceptions (a), (b), and (c). depending on
the occupancy of your wings these may apply. if using an exception i find
it useful to note the exception in my narratives and if commented on in the
response to the reviewer's comments.
On 1/3/11 1:05 PM, Peter Hillermann wrote:
Jeff,
We tried separating one of our buildings like that and the comment we got
from USGBC was.
7. The Baseline system type modeled does not seem consistent with the system
mapping from Table G3.1.1A. Please
confirm that the Baseline system was modeled correctly, or revise the system
type to reflect ASHRAE modeling protocol. Nonresidential
buildings which are five floors or less and between 25,000 and 150,000
sq.ft. should be modeled with System Type
#5 (fossil fuel heating) or System Type #6 (electric heating).
Thanks,
PETER HILLERMANN
peterh at westallarchitects.com
westall
architects
3404 pierce drive
chamblee, georgia 30341
o 770.458.4113
f 770.458.5352
c 678.898.2936
westallarchitects.com
Description: e-signatureDescription: USGBC-Logo
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff
Ross-Bain
Sent: Thursday, December 30, 2010 9:54 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline HVAC Type - Table G3.1.1 A&B (90.1-2007)
Hi All,
If a building has an overall area greater than 25,000 sq ft, but has
distinct wings each less than 25,000 sq ft and each has independent HVAC
systems, would one use System 6 (overall) or use System 4 (based on each
wing) to determine baseline type?
Thanks,
Jeffrey G Ross-Bain, PE, LEED, BEMP
Ross-Bain Green Building, LLC
404-228-2893
P Build Green...Save Time
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110328/7bdfff44/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2436 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110328/7bdfff44/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3222 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110328/7bdfff44/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3224 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110328/7bdfff44/attachment-0001.jpeg>