[Equest-users] f-factor & table a6.3 (90.1-2004 & 2007)
Patrick J. O'Leary, Jr.
poleary1969 at gmail.com
Wed Mar 23 20:14:24 PDT 2011
knowing that
1) appendix a, section 6.1, references that "For the purpose of Section
A1.2, the base assembly is a slab floor of 6 in. concrete poured
directly on to the earth ..." meets the requirement for an unheated slab
f-factor of 0.73, and
2) section a6.3, f-factors for slab-on-grade floors, a.6.3.1 states:
"/F-factors/ for slab-on-grade floors shall be taken from Table A6.3", and
3) section a6.3.2 states: "These /F-factors/ are acceptable for all
/slab-on-grade floors/."
does the "all slab-on-grade floors" really mean any thickness of
slab-on-grade? i.e. section 6.1 references a 6-inch uninsulated slab
meeting the 0.73 f-factor requirement, but per sections a6.3.2 and table
a6.3 a 4-inch uninsulated slab (or an 8-inch uninsulated slab) would
also meet the 0.73 f-factor requirement. so why would section a6.1
specify a 6-inch slab when any slab thickness will suffice? the user's
manuals (both years) just refer to table a6.3 for f-factor values.
the state of washington has a similar section in its energy code (see
link below), page 41, table 4-2. section 1003.2 (also page 41) lists
"All on-grade slab floors as assumed to be 6 inch concrete poured
directly onto the earth." note that on page 40, table 10.1, the
f-factors decrease the deeper the below grade the slab-on-grade floor is.
http://ftp.resource.org/codes.gov/wa_energy.pdf
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110323/816e891a/attachment.htm>
More information about the Equest-users
mailing list