Reducing the lighting power density is a easy for you and acceptable for
USGBC way.
On Tue, Mar 22, 2011 at 9:43 PM, <MatthewRLarson at eaton.com> wrote:
> Michael,
>
>
>
> There are a couple different ways to account for occupancy sensors for LEED
> but you need to follow Appendix G Table G3.2 of ASHRAE 90.1.
>
>
>
>
>
> Basically you’re allowed to reduce the lighting by the percentage listed in
> the above table, 10% for most buildings. You can do this by either reducing
> the lighting power input for the spaces by 10% under the Internal Loads tab
> or create a lighting occupancy sensor schedule that has hourly fractions
> that are 10% less than your regular lighting schedule. You also need to
> make sure that you apply this lighting credit to any spaces that are
> required by minimum code to have automatic lighting controls specified under
> Section 9.4.1. Table G3.1 Number 6 has a good explanation of this process
> for the baseline and proposed building.
>
>
>
> Thanks,
>
>
>
> *Matthew Larson, LEED AP BD+C
> *Project Engineer
>
> Energy Solutions Group**
>
> E M C Engineers, Inc.
> Eaton’s Electrical Services & Systems
> 143 Union Blvd, Suite 350
> Lakewood, CO 80228
> tel: +1 303 328-3419
> mobile: +1 303 668-2511
> fax: +1 303 974-1239
>
> MatthewRLarson at Eaton.com
> www.eaton.com/energysolutions
>
> [image: image001]
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *M. Shields
> *Sent:* Tuesday, March 22, 2011 6:24 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Lighting Controls for LEED
>
>
>
> Hi All,
>
>
>
> I just got back comments on my models for a LEED project and the reviewer
> commented that I needed to account for occupancy sensors. I had done this
> by switching the lighting schedule to the occupancy schedule in rooms with
> occupancy sensors, does anyone know if this is an appropriate way to model
> occupancy sensors? Is there a tool built into equest that allows you to
> account for them a different way?
>
>
>
> Thanks in advance,
>
>
>
> ____________________________
> Michael Shields
> Facility Strategies Group, LLC
>
> 1012 Market Street, Suite 307
>
> Fort Mill, SC 29708
>
> Phone: 803-493-4507
>
> Fax: 803-548-2511
> Email: mshields at fstrategies.com
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110323/5733a649/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14987 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110323/5733a649/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39998 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110323/5733a649/attachment-0001.jpeg>
More information about the Equest-users
mailing list