[Equest-users] Base Case building mutual shading
MatthewRLarson at Eaton.com
MatthewRLarson at Eaton.com
Mon Mar 14 07:33:04 PDT 2011
Anura,
This just means that one part of the building cannot shade another part
of the building. This is so this feature would be credited to the
proposed building when it is a beneficial design. The easiest way to do
this in eQuest is if you go to Building Shell and click on an Exterior
Wall in your Component Tree and click the spreadsheet tab, on the far
right side, the last column is "Shading Surface". Changing this to "No"
specifies that exterior wall not to shade any other surfaces of the
building. This input is also in the Exterior Surface Properties for an
Exterior Wall under the Daylighting - Shading - Other tab. It should be
noted that any shading by surrounding structures and topography should
be modeled identically in the baseline and proposed buildings.
Thanks,
Matthew Larson, LEED AP BD+C
Project Engineer
Energy Solutions Group
E M C Engineers, Inc.
Eaton's Electrical Services & Systems
143 Union Blvd, Suite 350
Lakewood, CO 80228
tel: +1 303 328-3419
mobile: +1 303 668-2511
fax: +1 303 974-1239
MatthewRLarson at Eaton.com <mailto:MatthewRLarson at Eaton.com>
www.eaton.com/energysolutions <http://www.eaton.com/energysolutions>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of anura
perera
Sent: Saturday, March 12, 2011 6:57 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Base Case building mutual shading
Dear All
It is stated that Base case building has to be modeled to avoid mutual
shading by the building itself. U shape and L shape are simple examples.
Can someone throw some ligth on this please.
Thanks in advance
Anura
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110314/c573f925/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39998 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110314/c573f925/attachment.jpeg>
More information about the Equest-users
mailing list