[Equest-users] VAV minimum flow

Nick Caton ncaton at smithboucher.com
Fri Mar 11 14:18:06 PST 2011


Hi there Xiaoyang,

 

VAV min flows can be set both in wizards and in detailed edit modes.
See following screenshots.

 

The "standard" depends on the HVAC design, and specifically how
ventilation air is being distributed.  There's a range of CFM's that the
factory will set as a minimum terminal unit at depending on the size,
but it may well be zero if you are distributing ventilation air via DOAS
in certain ways.  I'd suggest asking your HVAC designer directly what
the minimum is for each unit (it's probably scheduled), and use that
info to either come up with an average for each zone or to set the
minimum for each zone separately.

 

Here's the wizard...

 

... and in detailed, double click on a space served by a VAV system,
under the Airside HVAC tab, to find the following window.  In this case,
the minimum flow is set to 30% (0.30):

 

 

 

~Nick

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
xiaoyang shi
Sent: Friday, March 11, 2011 2:35 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] VAV minimum flow

 

Hi folks,

Do you know how to set the "VAV minimum flow" (percentage) at the "HVAC
zones: temperatures and Air Flows" panel? eQUEST default number is 40%.
Is there any standard?

Thank you.



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110311/00d12038/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110311/00d12038/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 20535 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110311/00d12038/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 21659 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110311/00d12038/attachment-0001.png>


More information about the Equest-users mailing list