[Equest-users] Inputting Elevator and Cooking Loads on Sub-Meters

James Hansen JHANSEN at ghtltd.com
Fri Mar 4 06:52:24 PST 2011


Assign the sub-meter to EM1.  Otherwise it will give you an error.  Open up the BDL file to troubleshoot errors like this.

-James

On Mar 4, 2011, at 9:24 AM, "Grayson Jordan" <grayson at castrucciarchitect.com> wrote:

> Hi,
> 
>  
> 
> I am attempting to show elevator and cooking loads on sub-meters so that I can demonstrate energy use for each of these loads discreetly.
> 
>  
> 
> I have attempted setting them up as direct loads, with corresponding schedule to the Misc. Loads.
> 
>  
> 
> I have set them up as Sub-Meters and as Building Meters.
> 
>  
> 
> eQuest allows me to set up one sub or building meter no problem.  When I add the second, I get an error and eQuest won’t run the simulation.
> 
>  
> 
> Any idea on how to troubleshoot?
> 
>  
> 
> Grayson Jordan, RA
> 
> Associate Architect
> 
>  
> 
> Paul A. Castrucci, Architect
> 
> 179 Rivington St., Suite 1A
> 
> New York, NY 10002 
> 
> voice: 212 254 7060 (ext 603)
> 
> fax:     212 260 7199
> 
>  
> 
>  
> 
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110304/c8dc2733/attachment.htm>


More information about the Equest-users mailing list