[Equest-users] Modeling Munters ERV in Equest

Shuichi Hendrickson Shuichi.Hendrickson at erm.com
Thu Mar 3 22:28:29 PST 2011


Kyle,

Im not familiar with Munters, but Im modelling a similar type of system using a Daikin Desica ERV here in Japan. The difference being that rather than an enthalpy wheel, the Desica has a multi-chamber crossflow HX with solid desiccant section. Rather than preheating exhaust air to regenerate the desiccant, the hot gas coils are actually imbedded in the desiccant for direct contact heating. There's a control damper that switches air flow from between the usable desiccant and desiccant undergoing regeneration sections.

I don't know of anyway to "accurately" model this system, but I am attempting to get a decent estimate given the limitations of the software. I doubt this is the magic bullet, but I'll explain what I'm doing:

I think you have to use the OA from system command to pull this off.  I set up a dummy zone with a CAV PSZ heat pump unit with solid desiccant pre treat and heat recovery. Make sure to get your supply temp dialled in, latent/sensible cooling capacity of your coils and don't double count your fan power. Set OA to 100% and your RH setpoint.

The "waste heat from compressor" issue is something that has driven me nuts for awhile since there appears to be no way to recover heat off the compressor for a heat pump in eQuest. Also, you need to reconcile if this is always going to be waste heat in the sense that will the heat pump ever operate primarily to regenerate desiccant or will it always be cooling first.  Basically I have come to 2 options

1)       Assign gas hydronic for regeneration. Define submeters for heat pump check your btuh hourly demand for gas and compare with hourly heat pump load. My assumption is that as long as the cooling load on the unit is greater than btus required for regeneration then regeneration is always waste heat and can be discounted, i.e. ignore the gas usage in your result reporting.
2)       This something that I am still toying with but it seems to work in principal. Build an air cooled heat pump chiller with compressor heat recovery (compressor heat recovery only seems to be available for chillers in eQuest). Assign the PSZ as a chilled water system and assign the desiccant regeneration to be hotwater off of your chiller. Discount and water pump energy for your water loops and make sure your performance curves are dialled into mimic your heat pump.

I would be interested to hear if anyone has tried anything similar or has comments on the above.

Cheers

Shuichi Hendrickson
Environmental Engineer, LEED AP

ERM Japan
The Landmark Tower
Yokohama 19F
2-2-1-1, Minatomirai, Nishi-ku
Yokohama, 220-8119, Japan

T:+81(0)45-640-3780
F:+81(0)45-640-3781
shuichi.hendrickson at erm.com<mailto:shuichi.hendrickson at erm.com>
www.erm.com<http://www.erm.com/>
Ranked No1 All-Environmental Firm: ENR Magazine (2004, 2005, 2006, 2007)
Environmental Adviser of the Year: Acquisitions Monthly (2005, 2006, 2008)
P Please consider the environment before printing this email



________________________________
From: Kyle Keith [mailto:kkeith at icthomasson.com]
Sent: Friday, March 04, 2011 1:41 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling Munters ERV in Equest

The Munters unit I am using is the Drycool Dehumidification System.  It is a 100% OA unit that I am using to feed several water source heat pumps room neutral air thus lowering the load on the heat pumps.  Outside air enters the Munters unit and passes through the top half of an Enthalpy wheel.  Return air from the space passes through the bottom of the wheel exchanging heat from one stream to the other.  The outside air is then pre-cooled with a DX coil then passes through a desiccant wheel.  The DH wheel is regenerated with the same return air stream as before after is has passes through a row of coils with heat from the compressors.  The supply air is now 76° 33% RH.  That air is then ducted to return plenums attached to each heat pump.

I know that I can use the "Outside air from system" option to supply the air to the heat pumps but I have yet to find a way to accurately model this unit, specifically the enthalpy wheel's position in the system and the desiccant wheel's regeneration source (waste heat from the compressor).  Admittedly I a new to equest but I have spent a considerable amount of time on the conundrum.  Any help would be greatly appreciated.

Kyle B. Keith
Mechanical
I. C. Thomasson Associates, Inc.
2950 Kraft Dr. Suite 500
Nashville, TN 37204
Phone: (615) 346-3498
Fax: (615) 346-3550
Email: kkeith at icthomasson.com<mailto:kkeith at icthomasson.com>
[cid:image001.jpg at 01CBDA80.CE8B5D20]



________________________________

This electronic mail message may contain information which is (a) LEGALLY PRIVILEGED, PROPRIETARY IN NATURE, OR OTHERWISE PROTECTED BY LAW FROM DISCLOSURE, and (b) intended only for the use of the Addressee (s) names herein. If you are not the Addressee (s), or the person responsible for delivering this to the Addressee (s), you are hereby notified that reading, copying, or distributing this message is prohibited. If you have received this electronic mail message in error, please contact us immediately and take the steps necessary to delete the message completely from your computer system. Thank you.

Please visit ERM's web site: http://www.erm.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110304/27d67993/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6212 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110304/27d67993/attachment.jpg>


More information about the Equest-users mailing list