[Equest-users] Default Values
Robby Oylear
robbyoylear at gmail.com
Wed Jul 27 14:49:11 PDT 2011
Bradley,
1. Don't know the answer to this question. What value are you trying to
restore to default in detailed mode? Jurisdiction has no effect on the
actual input of the detailed file as far as I know. Building type should
also not have any direct impact on the model, it just helps the wizard to
determine default values for other items (HVAC systems types available,
lighting and plug load values).
2. The infiltration values from the wizard are converted to a CFM/SF value
in detailed mode. There is no constant factor. Say you enter 0.05 CFM/SF
of wall area in the wizard and for a particular space this equates to 50
CFM. The wizard converts this to a CFM/SF number by dividing the calculated
infiltration value from your inputs (50 CFM) by the floor area of the space.
Hope this helps,
*Robby Oylear, LEED**®** AP BD+C*
*Mechanical Project Engineer*
*Energy Analyst*
* *
*D* 206-788-4571 | *C* 206-354-2721
*www.rushingco.com* <http://www.rushingco.com/>
On Wed, Jul 27, 2011 at 2:03 PM, Bradley Donohue <brad.donohue at me.com>wrote:
> Hello,
>
> I have two questions,
>
> 1. I was wondering where an equest model takes its default values from if
> it was completely constructed in the detailed mode. Because the modeler
> does not choose a building type or jurisdiction I am not sure where the
> values come from if you restore to default.
>
> 2. When changing from the wizard to detailed edit the infiltration values
> change to a by floor area number. What variable or factor does equest apply
> when making this automatic change?
>
> Thanks,
>
> Brad
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110727/25568f2a/attachment.htm>
More information about the Equest-users
mailing list