[Equest-users] Real Time Pricing / 8760 Utility Rate

Jeremy Poling Jeremy.Poling at transwestern.net
Mon Jul 25 11:52:48 PDT 2011


There is a "Energy Charge Schedule" keyword (ENERGY-CHG -SCH) on the
"Utility Rate Properties" dialog that accepts a schedule for hourly-use
schedules, but as David notes that is a rather complex utility rate to
model.  The help file says this about the keyword:

 

U-name of a SCHEDULE which specifies an ENERGY-CHG that varies by time
of day, week and/or season. The units in the schedule should be $/UNIT.
This schedule is used for all time-of-use energy billing (demand
time-of-use billing is more complex, and requires the use of multiple
BLOCK-CHARGEs). If both an ENERGY-CHG and ENERGY-CHG-SCH are defined,
the values will add.

That's all it says on this keyword, too...so if your consumption and
demand charges both are real-time pricing, there's quite a bit of work
ahead of you.

 

Jeremy R. Poling, PE, LEED AP+BDC



From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David
Eldridge
Sent: Monday, July 25, 2011 1:28 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Real Time Pricing / 8760 Utility Rate

 

Make an output report of the hourly building electricity
consumption/demand values that you need and do it in excel.  Probably
will be faster than making that complex of a schedule.

 

David

 


 

David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP

Grumman/Butkus Associates

 


 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Shea,
Rebecca
Sent: Monday, July 25, 2011 12:57 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Real Time Pricing / 8760 Utility Rate

 

I know that the joy of eQuest is that if you can schedule it, you can do
it.  However - can anyone give me a quick tutorial on how to assign an
8760 schedule as a utility rate?  I used the handy dandy "Energy Model
Input Translator" put out by RMI to generate my schedule
(http://www.rmi.org/rmi/ModelingTools) and then I imported the .inp file
into eQuest very nicely... now what? J (I made it a "multiplier"
schedule, not sure if that is correct, but I'm attaching it here.  I can
easily change the schedule type if necessary)

 

As always, any help appreciated.  Thanks for your valuable time,

Beka Shea

 

 

 

________________________________________________________________________
______________________ 
Rebecca Shea 
NORESCO 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110725/c57ef445/attachment.htm>


More information about the Equest-users mailing list