[Equest-users] baseline model HVAC equipment placing

Walson, Kristy kristy.walson at tlc-eng.com
Sat Jul 23 05:36:23 PDT 2011


Anura,

It depends on how large your building is and which version of ASHRAE  
you're using. For ASHRAE 90.1-2004, the baseline should have one  
system per thermal zone (even if you're proposed model is set up  
differently). If you're in ASHRAE 90.1-2007, up to a certain size  
building, it's still one system per thermal zone. After the threshold  
size, you're supposed to do one system for each floor of the building.  
I think the threshold size is 150,000 sq ft, but double check App.G to  
be sure.

Kristy

Be Green!  Sent from my iPhone.

On Jul 23, 2011, at 12:53 AM, "anura perera"  
<perera.anura25 at gmail.com> wrote:

> Dear All,
>
> I am modeling a Hotel in eQUEST for which the baseline HVAC system  
> type is PTHP. My proposed system has AHUs & FCs supplied by a  
> secondary pump circuit using chilled water.
>
> Can anyone indicate to me as to how I should plce my baseline system  
> (i.e on the basis of site, floor or thermal zones). The obvious  
> choice is thermal zones as per the proposed design.
>
> Thanks in adavnce
>
> Anura
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG


More information about the Equest-users mailing list