[Equest-users] eQUEST Sunspace
Jackson, Alan
ajackson at klingstubbins.com
Thu Jul 7 13:03:15 PDT 2011
Have you tried reverse laying the interior wall? If the interior wall was defined in the sunspace, then the material layer is reversed where the interior material is layer on the sunspace side and exterior is on the interior zone side.
O |<-GLASS [ S ] INT-SURFACE->||<-EXT-SURFACE [ I ]
U | [ U ] || [ N ]
T | [ N ] || [ T ]
D | [ S ] || [ . ]
O | [ P ] || [ Z ]
O | [ A ] || [ O ]
R | [ C ] || [ N ]
|<-GLASS [ E ] INT-SURFACE->||<-EXT-SURFACE [ E ]
So let's say your interior wall was brick faced. The brick surface would actually be the interior layer where normally it would be the exterior layer on a standard wall exposure. Put simpler âinsideâ is the side in the space in which the wall was defined.
See if that helps.
Alan Jackson, LEED AP
KlingStubbins
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ercoli, Christopher
Sent: Thursday, July 07, 2011 2:16 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQUEST Sunspace
Has anyone in the group used the sunspace option in eQUEST? I have tried it and it blew up in LOADS   Following is the .inp description of the Sunspace:
"EL1 North Perim Spc (G.N1)" = SPACEÂ Â Â Â Â Â Â Â Â Â
   X               = -25.25
  Y               = 109.6
  AZIMUTH         = 51.024
  SHAPE           = POLYGON
  ZONE-TYPE       = CONDITIONED
  PEOPLE-SCHEDULE = "EL1 Bldg Occup Sch"
  LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
  EQUIP-SCHEDULE  = ( "EL1 Bldg Misc Sch", "EL1 Bldg OffEq Sch",
         "EL1 Bldg OffEq Sch" )
  INF-SCHEDULE    = "ZG1-S1 (UVT) P-Inf Sch"
  INF-METHOD      = AIR-CHANGE
  INF-FLOW/AREA   = 0.0563044
  PEOPLE-HG-LAT   = 217.268
  PEOPLE-HG-SENS  = 250
  LIGHTING-W/AREA = ( 1.14175 )
  EQUIPMENT-W/AREA = ( 0, 0, 0.791 )
  SUNSPACE        = YES
  AREA/PERSON     = 165.463
  POLYGON         = "EL1 Space Polygon 1"
  C-SUB-SRC-BTUH  = ( 0, 0, 0 )
  C-SUB-SRC-KW    = ( 0, 0, 0 )
  C-ACTIVITY-DESC = *Office (Executive/Private) (79%)*
  ..
"EL1 North Wall (G.N1.E1)" = EXTERIOR-WALLÂ Â
   CONSTRUCTION    = "EL1 EWall Construction"
  LOCATION        = SPACE-V4
  SHADING-SURFACE = YES
  ..
"EL1 North Win (G.N1.E1.W1)" = WINDOWÂ Â Â Â Â Â Â Â Â
   GLASS-TYPE      = "EL1 Window Type #1 GT"
  FRAME-WIDTH     = 0.108333
  X               = 0.808333
  Y               = 0.938333
  HEIGHT          = 7.17333
  WIDTH           = 138.803
  FRAME-CONDUCT   = 1.306
  SPACER-TYPE     = INSULATED
  ..
"EL1 SW Wall (G.N1.I1)" = INTERIOR-WALLÂ Â
   NEXT-TO         = "EL1 WNW Perim Spc (G.WNW4)"
  CONSTRUCTION    = "Sunspace Wall construction"
  LOCATION        = SPACE-V1
  ..
"EL1 South Wall (G.N1.I2)" = INTERIOR-WALLÂ Â
   NEXT-TO         = "EL1 Core Spc (G.C5)"
  CONSTRUCTION    = "Sunspace Wall construction"
  INT-WALL-TYPE   = STANDARD
  LOCATION        = SPACE-V2
  ..
"Sunspace Window" = WINDOWÂ Â Â Â Â Â Â Â Â
   GLASS-TYPE      = "EL1 Window Type #1 GT"
  X               = 1
  Y               = 6.5
  HEIGHT          = 2
  WIDTH           = 122
  C-WELL-HEIGHT   = 6.5
  C-WELL-WIDTH    = 1
  ..
"EL1 SSE Wall (G.N1.I3)" = INTERIOR-WALLÂ Â
   NEXT-TO         = "EL1 SE Perim Spc (G.SE2)"
  CONSTRUCTION    = "Sunspace Wall construction"
  LOCATION        = SPACE-V3
  ..
"EL1 Ceiling (G.N1.I4)" = INTERIOR-WALLÂ Â
   NEXT-TO         = "EL1 North Perim Plnm (G.N6)"
  CONSTRUCTION    = "Air Ceiling of Sunspace"
  INT-WALL-TYPE   = AIR
  LOCATION        = TOP
  ..
"EL1 Flr (G.N1.U1)" = UNDERGROUND-WALL
  CONSTRUCTION    = "EL1 UFCons (G.N1.U2)"
  LOCATION        = BOTTOM
  ..
Following is the system description of the sunspace:
"EL1 North Perim Zn (G.N1)" = ZONEÂ Â Â Â Â Â Â Â Â Â Â
   TYPE            = CONDITIONED
  MIN-FLOW-RATIO  = 1
  BASEBOARD-RATING = -25605.4
  FLOW/AREA       = 0.25
  OA-FLOW/PER     = 18.2732
  SS-FLOW-T-SCH   = "Max T for SS heating Annual"
  SS-VENT-CST     = 5
  SS-VENT-WND     = 0.2
  SS-VENT-TEMP    = 0.2
  SS-VENT-T-SCH   = "Vent T Annual Schedule"
  SS-VENT-SCH     = "Sunspace Venting Schedule"
  DESIGN-HEAT-T   = 72
  HEAT-TEMP-SCH   = "S1 Sys1 (UVT) Heat Sch"
  DESIGN-COOL-T   = 75
  BASEBOARD-CTRL  = THERMOSTATIC
  SIZING-OPTION   = ADJUST-LOADS
  SPACE           = "EL1 North Perim Spc (G.N1)"
  ..
"EL1 North Perim Pl Zn (G.N6)" = ZONEÂ Â Â Â Â Â Â Â Â Â Â
   TYPE            = UNCONDITIONED
  DESIGN-HEAT-T   = 67
  DESIGN-COOL-T   = 75
  SIZING-OPTION   = ADJUST-LOADS
  SPACE           = "EL1 North Perim Plnm (G.N6)"
Following is the error message
***ERROR***********************************************************************
In routine TEMDEV for ZONE EL1 North Perim Pl Zn (G.N6)    on 2/10 hr 11 (InitialFlg = 0)
 SUNSPACE INTERIOR-WALL calculations produced bad values:
 CSSVEC (convection) =          0. CSSVEC (conduction) =    7294864.
 This would cause a 262. degree ZONE temperature change.  Values are being ignored.
 Check wall definitions for errors and report this inp/lib/wth to DOE-2 support.
***ERROR***********************************************************************
In routine TEMDEV for ZONE EL1 North Perim Zn (T.N11)      on 2/10 hr 11 (InitialFlg = 0)
 SUNSPACE INTERIOR-WALL calculations produced bad values:
 CSSVEC (convection) =          0. CSSVEC (conduction) =  176604512.
 This would cause a 6794. degree ZONE temperature change.  Values are being ignored.
 Check wall definitions for errors and report this inp/lib/wth to DOE-2 support.
Any ideas as to where I went wrong?
- Christopher ErcoliÂ