[Equest-users] my math on DWH efficiency?

Nick Caton ncaton at smithboucher.com
Wed Jul 6 13:20:11 PDT 2011


Hmm… I read this quickly and it seemed off so I double checked:

TANK-UA

The overall heat loss coefficient (UA) of the heater. The heat loss is calculated as this value times the temperature difference between the water in the heater and the environmental temperature. 

 

You got the 90.1 calc right:  SL = 20 + 35*sqrt(240) = 562 

 

Rephrasing the DOE2 help entry copied above:  SL = UA * delta-T

 

Set:  562 = UA * 70

 

Then: UA = 562/70 = 8.03

 

As I understand it, TANK-UA rolls together the properties of both the insulation and surface area, so given TANK-UA you shouldn’t need to work in the tank volume or area to find the standby loss for a given delta-T.  That’s my take – hope it helps =)!

 

~Nick

 

 

 

 

NICK CATON, P.E.

SENIOR ENGINEER

 

Smith & Boucher Engineers

25501 west valley parkway, suite 200

olathe, ks 66061

direct 913.344.0036

fax 913.345.0617

www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James Hansen
Sent: Wednesday, July 06, 2011 10:31 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] my math on DWH efficiency?

 

I had a question about calculating baseline 90.1 efficiency for electric DWHs (tank type).

 

Based on Table 7.8, my efficiency needs to be SL = 20 + 35*sqrt(V) at a 70 degree delta T between water and ambient, where SL is the standby loss in btuh, and V is the volume of the tank.

 

If, in my proposed model, I have a 240 gallon tank (meaning my baseline has the same volume), it would appear that the maximum standby loss at a 70 degree delta should be 562 btuh [20 + 35 * sqrt(240)]

 

Since eQuest calculates the heat loss by multiplying the UA (thermal conductivity of storage tank) by the tank, it would appear that my UA for this particular example would be 562 / (70*240), or 0.0334.

 

That way, at a 70 degree delta, the heat loss (SL) would be 0.0334 Btu/hr-gal-F * 240 gallons * 70 F = 562 btuh

 

Does that sound about right?  

 

Thanks to anyone that has a quick chance to review!

 

GHT Limited
James Hansen, PE, LEED AP

Senior Associate

1010 N. Glebe Rd, Suite 200

Arlington, VA  22201-4749

703-338-5754 (Cell)

703-243-1200 (Office)

703-276-1376 (Fax)

www.ghtltd.com <http://www.ghtltd.com/> 

 

 

________________________________

The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com <mailto:ght at ghtltd.com> , and destroy this communication and all copies thereof, including all attachments.  Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110706/2b97fbec/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110706/2b97fbec/attachment.jpeg>


More information about the Equest-users mailing list