[Equest-users] Unable to assign a VAV "terminal type"
Paul Diglio
paul.diglio at sbcglobal.net
Tue Jul 5 03:58:23 PDT 2011
Rob:
Right-click on the gray area in VAV Terminal Type. Chose Edit/View User
Default, click User Defined Default Value and use the drop down arrow to choose
your VAV type.
To verify that the VAV terminal device is operating correctly, create a new
Thermal Zone Type Hourly Report Block for the VAV zone. It will verify that the
VAV box is varying the airflow.
Paul Diglio
________________________________
From: Rob S. Young <youngrs at kjww.com>
To: Carol Gardner <cmg750 at gmail.com>
Cc: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Mon, July 4, 2011 2:24:03 PM
Subject: Re: [Equest-users] Unable to assign a VAV "terminal type"
System Type is VAVS.
Thanks,
Rob
Rob Young, PE
Mechanical Engineer | youngrs at kjww.com
2882 106th St | Des Moines, IA 50322
515.334.9906 | Direct: 515.334.4311 | Fax: 515.334.9908
www.kjww.com
From:Carol Gardner [mailto:cmg750 at gmail.com]
Sent: Monday, July 04, 2011 11:40 AM
To: Rob S. Young
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Unable to assign a VAV "terminal type"
What are you calling your system type? It will have to be VAVS, PVAVS or PVVT to
be able to include VAV boxes.
Carol
On Mon, Jul 4, 2011 at 9:12 AM, Rob S. Young <youngrs at kjww.com> wrote:
I am working on a model for a project where multi-zone air handling systems are
being converted to single-duct VAV systems. I have already completed the system
changes so that all of the air handling units are single-duct VAV. However, I
am unable to change the zones to include VAV boxes. Under each zone in the "Air
Flow" tab, the "Zone Terminal and Fans" section is all grayed out and will not
allow any changes. I tried deleting the zone and re-creating it, but I still
have the same issue. Any advice is much appreciated!
Rob
This message and any attachments contain information intended for a specific
party and may include sensitive or confidential material. If you are not the
intended recipient, please do not read, copy, use, or disclose to others.
Please notify the sender of the delivery error by reply and then permanently
delete this message and all attachments.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
________________________________
This message and any attachments contain information intended for a specific
party and may include sensitive or confidential material. If you are not the
intended recipient, please do not read, copy, use, or disclose to others.
Please notify the sender of the delivery error by reply and then permanently
delete this message and all attachments.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110705/1f7517f2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 7768 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110705/1f7517f2/attachment.jpg>
More information about the Equest-users
mailing list