[Equest-users] LEED review comments for System 5 heating source
Paul Diglio
paul.diglio at sbcglobal.net
Fri Jul 1 07:06:52 PDT 2011
Lan:
In the Advanced Energy Modeling for LEED Technical Manual v.1 page 28 under
ASHRAE 90.1-2004 common errors for HVAC System, primary system type, the second
error is 'Baseline HVAC systems use both fossil fuel and electricity'.
I assume this is why your reviewer requested that the baseline be changed to the
predominate heating energy source that was used in the proposed model.
Paul Diglio
________________________________
From: "Li, Lan" <lli at sbmce.com>
To: Paul Diglio <paul.diglio at sbcglobal.net>; cmg750 at gmail.com;
Paul.Riemer at dunhameng.com
Cc: equest-users at lists.onebuilding.org
Sent: Fri, July 1, 2011 9:45:38 AM
Subject: RE: [Equest-users] LEED review comments for System 5 heating source
Paul, Paul and Carol,
This sentence just jumps into my eyes. It is on ASHREA 90.1-2007 User’s manual
page G-22.
Here is the interception.
The performance rating rules for the baseline building HVAC system are shown in
Table G-A. This table shows the baseline building system types, based on
building type (nonresidential or
residential), the number of floors, the floor area and the heating source
(electric or other). Note that a hybrid system refers to a system with any
combination of fossil and electric heat, and the baseline system for this is a
fossil fuel system.
I think I will stick with my gun and go for it. I will keep all of you posted
for the outcome of my review. Hopefully everyone will be clear on this matter
then.
Thanks!
Lan
Lan Li, PE, LEED AP BD+C
Mechanical Engineer
Scheeser Buckley Mayfield LLC
1540 Corporate Woods Parkway
Uniontown, OH 44685
Phone: (330) 896-4664 ext. 123
Fax: (330) 896-9180
Cell:(330) 904-6292
lli at sbmce.com
www.sbmce.com
ColumbusOffice (614) 448-1498
üPlease consider the environment before printing this email.
This e-mail (including any attachments) is confidential and may be legally
privileged. If you are not an intended recipient or an authorized representative
of an intended recipient, you are prohibited from using, copying or distributing
the information in this e-mail or its attachments. If you have received this
e-mail in error, please notify the sender immediately by return e-mail and
delete all copies of this message and any attachments.
Thank you
________________________________
From:Paul Diglio [mailto:paul.diglio at sbcglobal.net]
Sent: Thursday, June 30, 2011 5:48 PM
To: Li, Lan; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] LEED review comments for System 5 heating source
Lan:
90.1-2007 requires a system 5 with a fossil fuel hot water boiler as you have
modeled, but in 90.1-2007 Table G3.1 Number 10 HVAC Systems Base Building
Performance column it states that you need to meet any system-specific
requirements in Section G3.1.3.
In G3.1.3.2, it states that for system 5, the boiler plant shall use the same
fuel as the proposed design, which in your case is electric resistance and
compressor heat pump energy. I would model electric hot water boilers.
Paul Diglio
________________________________
From:"Li, Lan" <lli at sbmce.com>
To: equest-users at lists.onebuilding.org
Sent: Thu, June 30, 2011 4:24:27 PM
Subject: [Equest-users] LEED review comments for System 5 heating source
Dear eQuesters,
I just got LEED review comments for my project. Our proposed design is VRF
system with roof top unit providing ventilation air. Roof top unit is using gas
as heating source. There are misc. elec. heaters in the building for places like
entries. I interpreted my building heating source as “electric hybrid” and used
hot water fossil fuel boiler as my base design. The comments I got read as the
follows:
Section 1.1.A of the form indicates that the primary heating source is fossil
fuel. However, the electric heating energy use reported in Table EAp2-5 for the
Proposed Case exceeds the fossil fuel heating energy use. Please verify that the
correct heating source has been selected. If electric heating is the primary
heating source, please change the Baseline system type accordingly. Provide
updated simulation results and a revised Prerequisite Form as necessary.
I couldn’t find an official definition either on LEED reference book or 90.1.
What is your take on this?
Your input is highly appreciated! Thank you very much!
Lan
Lan Li, PE, LEED AP BD+C
Mechanical Engineer
Scheeser Buckley Mayfield LLC
1540 Corporate Woods Parkway
Uniontown, OH 44685
Phone: (330) 896-4664 ext. 123
Fax: (330) 896-9180
Cell:(330) 904-6292
lli at sbmce.com
www.sbmce.com
ColumbusOffice (614) 448-1498
üPlease consider the environment before printing this email.
This e-mail (including any attachments) is confidential and may be legally
privileged. If you are not an intended recipient or an authorized representative
of an intended recipient, you are prohibited from using, copying or distributing
the information in this e-mail or its attachments. If you have received this
e-mail in error, please notify the sender immediately by return e-mail and
delete all copies of this message and any attachments.
Thank you
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110701/297df50a/attachment.htm>
More information about the Equest-users
mailing list