[Equest-users] Underground soil temperature
Mehta, Gaurav
Gaurav.Mehta at stantec.com
Tue Jan 25 09:09:12 PST 2011
Omar,
The LS-C report shows substantial sensible cooling load (~ 30%) from the Underground Surface Conduction which is alarming. Check the construction and ensure that you are modeling it correctly. If you are modeling it as U-value input, then it might be a good idea to change it to the Layer Input.
It might be possible that there is an error in the weather file. If you have the weather file (TMY2 or TMY3) in epw format then you can use Climate Consultant software (download for free from: http://www.energy-design-tools.aud.ucla.edu/) to view the ground temperatures.
OR
Create an hourly report in eQUEST.
See DOE-2 help:
Volume 4: Libraries & Reports > Reports > Hourly-Report and REPORT-BLOCK
And click on GLOBAL, the Variable List number 2 is listed as TGNDR (Ground Temperature [Rankine]).
I have no clue at what depths these temperatures are reported but please keep in mind that it is not necessary that the ground temperatures are always constant, they do experience some variability throughout the year.
Thanks.
Best regards,
Gaurav
Gaurav Mehta, LEED® AP BD+C
Sustainable Building Analyst
Stantec
1932 First Avenue Suite 307
Seattle WA 98101
Ph: (206) 770-7779
Fx: (206) 770-5941
Gaurav.Mehta at stantec.com
stantec.com<http://www.stantec.com>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar Katanani
Sent: Tuesday, January 25, 2011 2:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Underground soil temperature
Dear all,
Is there any way to view the contents of the weather file?
I would like to check the underground soil temperature. This is because more than half of my vertical walls are buried into the ground (I've modelled them as below grade walls).
However, I'm getting a lot of heat transfer into the building from the underground walls, meaning that the soil is at temperatures much higher than 25 C. (Please check attached document!!)
As far as I know, the underground should be at a more or less constant temperature of around 20C throughout the year...
Many thanks,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net<mailto:omar at ecoconsulting.net>
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 266
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net<http://www.ecoconsulting.net/>
[cid:image001.jpg at 01CBBC69.8DB63E30]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110125/4a793409/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 27542 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110125/4a793409/attachment.jpg>
More information about the Equest-users
mailing list