[Equest-users] Constructing chiller part load curves
Nick Caton
ncaton at smithboucher.com
Wed Jan 19 09:00:37 PST 2011
Hi Afaan,
The first table below contains the sort of information you will need to
make a centrifugal EIR curve, but as David says you're lacking in the
minimum # of data points. I believe the bare minimum to extrapolate an
accurate bi-quadratic curve would require 9 rows of data (minimum 3
PLR's for a minimum 3 dT's), though you should probably use the maximum
number of data entry points permitted when allowing eQuest to determine
the coefficients (20 per curve).
dT is simply the difference between the chilled and condenser water
temps.
I'm not sure exactly what we're looking at in the second table, but it
doesn't look like data for creating a curve... If you want to make
CAP-FT and EIR-FT curves (and if you don't, that's okay too - see below)
you'll need a rep who understands and can provide you with "maximum
capacity" (not the designed capacity, or where PLR = 1.0) and power
drawn under different conditions. I've previously selected 5 CW temps
and 4 CHW temps around and including the design conditions being
normalized to, totaling the maximum 20 data entry points we're permitted
to input.
The attached email contains an overview of materials you should review
to understand the process of custom chiller curve creation (includes a
reference to the same EDR guideline David brings up below). Once you
feel comfortable understanding the required data collection described
towards the end of the referenced EDR chapter, you might do well to also
read through a fairly lengthy discussion on this list that I started:
"Chiller Curves (oh boy!)." There, I eventually provided an
illustrated breakdown of each default curve and its
function/implications, eventually realizing and providing visuals of
their combined effects analogous to what equipment reps often provide
for "chiller efficiency curves." You should be able to follow this
discussion from start to finish, and should come away knowing exactly
what eQuest is doing "under the hood" moving forward. Carol Gardner
also provided a writeup within that discussion that is similar to the
EDR... oh I see she just posted it again =)!
One final suggestion: Your collected data suggests a possible pitfall -
if you want to make the CAP-FT and EIR-FT curves, you MUST gather data
for multiple CHW temps, even if the design should only ever call for 44
degree water to be produced. If you don't understand why, then honestly
you need further review of what the curves are functionally doing - see
suggested reading above and attached.
If you and your reps are struggling with producing the data required to
make CAP-FT and EIR-FT curves, it's advisable to stick with the
defaults, and ensure your custom EIR-fPLR&dT curve entries are all
normalized to ARI rather than a design condition.
Best of luck!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David
Eldridge
Sent: Wednesday, January 19, 2011 7:38 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Constructing chiller part load curves
You may want to run through this document before you get too much
further. Skip ahead to "Part 2" of the document.
http://www.energydesignresources.com/media/2654/EDR_DesignGuidelines_%20
HVAC_Simulation.pdf
In a nutshell - you should acquire a few more data points to develop a
more comprehensive matrix. Right now your matrix would be equivalent to
a line through the middle of possible conditions, you need to extend
your data set over a wider range of water temperatures and load
conditions.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, HBDP
Project Manager
Direct: (847) 316-9224 | Fax: (847) 328-4550
http://www.grummanbutkus.com
Grumman/Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL
60201
Energy Efficiency Consultants and Sustainable Design Engineers
From: equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] On Behalf Of Afaan Naqvi
Sent: Tuesday, January 18, 2011 8:33 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Constructing chiller part load curves
After browsing the forums, it seems there are many users that have
constructed custom chiller curves based on selection data. I believe I
have all the data I need to do this, but am coming up with polynomial
coefficients and hourly results that do not make sense at all. Can
someone please walk me through how to go about building the 3 curves for
a centrifugal, water cooled chiller with a VSD based on the following
data:
% Load
Capacity
kW in
Perf
Evap T in
Evap T out
Conden T in
Coned T out
100
85
53.6
0.63
54
44
85
94.8
75
63.8
29.8
0.47
51.5
44
75
82
50
42.5
13.3
0.31
49
44
65
69.5
25
21.3
6.9
0.32
46.5
44
65
67.2
I believe the additional data I need is calculated below, except for the
dT term which I am unclear on:
Load
PLR
kW
f PLR
85
1
53.6
1
63.8
0.751
29.8
0.556
42.5
0.500
13.3
0.248
21.3
0.251
6.9
0.129
Not sure if the dT term required by the curves is the difference in
condenser supply and return, or condenser and evaporator supply,
condenser supply and evaporator return, etc. Can someone please clarify?
Thanks
Afaan Naqvi PE LEED AP
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110119/296c0a8b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110119/296c0a8b/attachment.jpeg>
-------------- next part --------------
An embedded message was scrubbed...
From: "Nick Caton" <ncaton at smithboucher.com>
Subject: Re: [Equest-users] Electricity consumption by CHILLER
Date: Fri, 5 Nov 2010 09:12:24 -0600
Size: 34593
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110119/296c0a8b/attachment.eml>
More information about the Equest-users
mailing list