[Equest-users] Baseline HVAC Type - Table G3.1.1 A&B (90.1-2007)

Jeremy Poling Jeremy.Poling at transwestern.net
Tue Jan 4 06:16:15 PST 2011


I would also recommend checking the standards interpretations on
ASHRAE's website (http://www.ashrae.org/technology/page/121) since there
are a few that apply to those exceptions.  The exceptions haven't
changed between 2004 and 2007 so look at both for official
interpretations of when to use those exceptions.

 

In applying those exceptions, the baseline system from Table G3.1.1 must
still be used for the predominant condition, held by ASHRAE and the
USGBC/GBCI to mean the portion of the building with the larger square
footage (i.e. the office portion of a warehouse is not the predominant
condition).  So even if one of the exceptions applied for your building,
you would still have to model at least a portion of the building with
the standard baseline from Table G3.1.1. (Peter - that is what the
reviewers did not say, probably to stay clear of the GBCI's rule about
not offering design advice).

 

Jeffrey - Table G3.1.1 is intended to apply to entire buildings, so
unless the two wings are completely separate with no shared party walls,
systems, foundations, etc. it will probably be difficult to get the
reviewers to accept using a different baseline for both of the wings.
If one of the exceptions does apply, it may be useful on one of the
wings, but the submittal should include a detailed explanation of why
the exception applies so the reviewers can understand the circumstances
better - they tend to view the exceptions as being more or less rare.

 

Jeremy R. Poling, PE, LEED AP+BDC



 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Patrick
J. O'Leary, Jr.
Sent: Tuesday, January 04, 2011 6:11 AM
To: Peter Hillermann
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline HVAC Type - Table G3.1.1 A&B
(90.1-2007)

 

see appendix g, section g3.1.1, exceptions (a), (b), and (c).  depending
on the occupancy of your wings these may apply.  if using an exception i
find it useful to note the exception in my narratives and if commented
on in the response to the reviewer's comments.

On 1/3/11 1:05 PM, Peter Hillermann wrote: 

Jeff,

 

We tried separating one of our buildings like that and the comment we
got from USGBC was...

 

7. The Baseline system type modeled does not seem consistent with the
system mapping from Table G3.1.1A. Please

confirm that the Baseline system was modeled correctly, or revise the
system type to reflect ASHRAE modeling protocol. Nonresidential

buildings which are five floors or less and between 25,000 and 150,000
sq.ft. should be modeled with System Type

#5 (fossil fuel heating) or System Type #6 (electric heating).

 

Thanks,

 

PETER HILLERMANN

 

peterh at westallarchitects.com

 

westall

architects

3404 pierce drive

chamblee, georgia 30341

 

o 770.458.4113

f  770.458.5352

c 678.898.2936

 

westallarchitects.com

  

 

From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff
Ross-Bain
Sent: Thursday, December 30, 2010 9:54 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline HVAC Type - Table G3.1.1 A&B
(90.1-2007)

 

Hi All,

 

If a building has an overall area greater than 25,000 sq ft, but has
distinct wings each less than 25,000 sq ft and each has independent HVAC
systems, would one use System 6 (overall) or use System 4 (based on each
wing) to determine baseline type? 

 

Thanks,

 

Jeffrey G Ross-Bain, PE, LEED, BEMP

Ross-Bain Green Building, LLC

404-228-2893

 

P Build Green...Save Time

 

 

 

 
 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to 
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
  

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110104/1a0ec666/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3224 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110104/1a0ec666/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2436 bytes
Desc: image002.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110104/1a0ec666/attachment.gif>


More information about the Equest-users mailing list