[Equest-users] Building Shades
John T. Forester
JohnTF at BVHis.com
Mon Jan 3 12:47:30 PST 2011
If you are in the detailed edit mode and double-click on an exterior wall or roof and the second properties tab (Daylighting - Shading - Other) will show you if that surface is a shading surface or not. You can alternatively review all of your external constructions in the spreadsheet view (also in detailed edit mode). It is the last column in the spreadsheet.
Coming from the wizard, you can go into detailed edit mode and check to see how the construction in being handled then return to the wizard without losing anything as long as no changes are made in the detailed edit mode. If you right click in the field and then choose Item Help, you can read about how eQuest handles this input variable.
[cid:image001.png at 01CBAB5D.30C3AEF0]
John T. Forester, P.E., LEED AP, Mechanical Design Engineer I BVH Integrated Services I 617.658.9008 tel I 617.244.3753 fax I One Gateway Center Suite 506, Newton MA 02458 I www.bvhis.com<http://www.bvhis.com> I Hartford ● New Haven ● Boston
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob Hudson
Sent: Monday, January 03, 2011 3:34 PM
To: Jonathan Bowser
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Building Shades
that is my assumption as well. i haven't truly modeled two separate buildings before for a project, but i did try a litmus test model once.
what i did was created two shells one north of the other and looked at the output reports for solar loads on the southern faces. the northern one did have a smaller load on the southern face, which leads me to believe that this part of eQuest works just fine. if anyone has an actual project that they can speak of then that would be a better answer, but for now this is what i got,
Rob
On Mon, Jan 3, 2011 at 3:31 PM, Jonathan Bowser <JonathanBowser at beck-technology.com<mailto:JonathanBowser at beck-technology.com>> wrote:
Thanks for the quick response, Rob. For my own sanity, could I have something else clarified as well?
I’ve always been under the assumption that if I model multiple shells in the wizard, the shading effects of the shells are taken into account when performing the analysis. Is this actually the case?
Note: I understand this isn’t the same thing as creating a building shade in the detailed edit mode since I’m actually introducing more components into the analysis.
-- Jon
Jonathan Bowser
Senior Software Engineer
Beck Technology
1807 Ross Avenue, Suite 500
Dallas, TX 75201
(214) 303-6815
www.beck-technology.com<http://www.beck-technology.com/>
Innovation in All Dimensions
Please consider the environment before printing this e-mail
This e-mail may be privileged and confidential. If you are not the intended recipient, please delete from all computers.
________________________________
From: Rob Hudson [mailto:rdh4176 at gmail.com<mailto:rdh4176 at gmail.com>]
Sent: Monday, January 03, 2011 2:24 PM
To: Jonathan Bowser
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Building Shades
You cannot do this through the wizards, it must be done in the detailed edit mode after the wizard has been completed. shades are easy to inpliment as long as you have the information (size and orientation) of the surrounding buildings readily available.
hope this helps!
Rob
On Mon, Jan 3, 2011 at 3:19 PM, Jonathan Bowser <JonathanBowser at beck-technology.com<mailto:JonathanBowser at beck-technology.com>> wrote:
After searching through the archive, I’ve learned I can create Building Shades in the detailed mode in eQUEST. Is it possible to do something similar through one of the wizards?
Essentially I’d like a quick, easy way of modeling surrounding buildings so that their shading effects are taken into account.
-- Jon
Jonathan Bowser
Senior Software Engineer
Beck Technology
1807 Ross Avenue, Suite 500
Dallas, TX 75201
(214) 303-6815
www.beck-technology.com<http://www.beck-technology.com/>
Innovation in All Dimensions
Please consider the environment before printing this e-mail
This e-mail may be privileged and confidential. If you are not the intended recipient, please delete from all computers.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Rob Hudson
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110103/8c892661/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 19007 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110103/8c892661/attachment.png>
More information about the Equest-users
mailing list