[Equest-users] why pump consume less energy
Grammy
grammy.hkust at gmail.com
Mon Jan 3 04:30:13 PST 2011
Hi, Zhiren,
The "pump properties" window show that the pump has a *85* mech eff,
very impressive.
Check your equipment list and find the right mech eff. to input - I guess
the pump eff. should be 85%, not 8500%.
2011/1/3 周志仁 <zhouzr at cabr-sh.com>
> Dear all
>
> My proposed model consume much less pump energy which is less than
> 1% of the total energy. There are 10 chiller and 10 pumps(all are VSD) in
> the proposed. The figure below shows the breakdown of total energy
> consumption, the pump is very low. The pump setting is shown in the second
> figure below.
>
> Why the loop head is given in the SIM file as shown in the third figure
> below? Why the pump consume little energy? Can anyone tell me the reason?
> Thanks a lot.
>
>
>
>
> Yours arron
>
>
>
> [image: cid:image002.jpg at 01CBAB75.979D1A90]
>
>
>
> [image: cid:image004.png at 01CBAB74.C92BFB90]
>
>
>
> [image: cid:image005.png at 01CBAB75.979D1A90]
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110103/0b570ae8/attachment.htm>
More information about the Equest-users
mailing list