[Equest-users] Process flow on hot water loop
Fleming, Joe
joe.fleming at tlc-eng.com
Tue Feb 22 08:52:39 PST 2011
You need to assign a process "load" other than 0.00. Equest uses the load on the coils for its calcs, and will not use flow rates in the process area unless it is a DHW system.
If you want to add a process load then the "process load" needs to be calc'd out manually and input. The flow rate is an additional input to the process load that will add to pumping power. If no load is input than the flow rate will have no effect.
Good Luck!
Joe Fleming
E.I., LEED AP BD+C, BEMP
Mechanical Engineer II
TLC Engineering for Architecture
Your 2030 Challenge Partner
800 Fairway Drive, Suite 250
Deerfield Beach, FL 33441-1816
phone:
954-418-9096
fax:
954-418-9296
direct:
954-418-4591
website:
www.tlc-engineers.com<http://www.tlc-engineers.com/>
[cid:image001.gif at 01CBD286.99098660]<http://www.tlc-engineers.com/>
From: R B [mailto:slv3sat at gmail.com]
Sent: Tuesday, February 22, 2011 11:30 AM
To: Fleming, Joe
Cc: eQUEST Users List
Subject: Re: [Equest-users] Process flow on hot water loop
Here are the input file. Thanks
-Rohini
On Tue, Feb 22, 2011 at 10:03 AM, Fleming, Joe <joe.fleming at tlc-eng.com<mailto:joe.fleming at tlc-eng.com>> wrote:
Could be a few things, you might need to upload your .inp file for this one.
Joe Fleming
E.I., LEED AP BD+C, BEMP
Mechanical Engineer II
TLC Engineering for Architecture
Your 2030 Challenge Partner
800 Fairway Drive, Suite 250
Deerfield Beach, FL 33441-1816
phone:
954-418-9096
fax:
954-418-9296
direct:
954-418-4591
website:
www.tlc-engineers.com<http://www.tlc-engineers.com/>
[https://mail.google.com/mail/?ui=2&ik=127ac437df&view=att&th=12e4e2af56e1b823&attid=0.1&disp=emb&realattid=84f32d19ccfef641_0.1&zw]<http://www.tlc-engineers.com/>
From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of R B
Sent: Tuesday, February 22, 2011 11:00 AM
To: eQUEST Users List
Subject: Re: [Equest-users] Process flow on hot water loop
I sent this message yesterday but it did not show up on the list - so here it is again.
I am simulating the domestic hot water consumption as process flow on the hot water loop. But it is not showing up in the results (the beps report is same with 0 gpm vs 11.1 gpm, and the schedule is non-zero). Am I missing something or is there a bug?
-Rohini
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110222/c8a9950e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 5272 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110222/c8a9950e/attachment.gif>
More information about the Equest-users
mailing list