[Equest-users] how to model 40% glazing on baseline
Nick Caton
ncaton at smithboucher.com
Mon Feb 21 14:10:01 PST 2011
There's a few opinions on "best" approach... every case is unique, but
here's general my take:
- Figure out your gross window-wall-ratio (WWR) for the whole
building. Let's say it's 60% for illustration.
- If the WWR < 40%, your baseline can simply use the same
window layout defined in the proposed model, and this would be a moot
concern
- If the WWR > 40%, divide the two to figure a window area
"correction factor:" 40%/60% = .6667
- Assuming you're post-wizards and in detailed edit mode:
You'll multiply the height dimension of all windows in your proposed
model by that correction factor... (width works too, but height is
generally better - I'll explain)
o Highlight a window under the Building shell tab
o Switch to spreadsheet view
o Highlight the column containing the window heights (use shift+arrow
keys here)
o Ctrl+c
o Open excel
o Ctrl+v in A1
o In B1: =A1*.6667
o Drag that down to get all your new values
o Rearrange your windows on your computer screen so you can see the
excel column and the equest column side-by-side
o You probably are using a common height for many/most windows. Right
click any value -> edit user default - click the radio button that lets
you define a number, and input that most common (reduced) value in your
"factored" excel column
o Right click any equest cell and press 'r' to restore default - value
will turn blue to represent a 'user-default' (instead of a green DOE2
default)
o Ctrl+c that defaulted cell
o Now start from the top and play accountant: enter the value, press
the down arrow key, rinse and repeat. Anytime you see the common
default value, just ctrl+v.
- Once you're done, the WWR of your baseline will be adjusted
down to match 40%, and you'll have maintained the same WWR on each
orientation as your proposed model.
If you're building your baseline from the wizards on up, you could also
achieve uniform bands on each face totaling 40% net by playing with the
inputs in the right shell screens. This was once a prescribed approach
that was removed from Appendix G's wording in 90.1-2007, but it remains
a viable approach as well. The potential disadvantage to this approach
is you're changing the individual WWR for each individual space (perhaps
adding windows where there were none) - this may result in less of an
"apples to apples" comparison between the models, which may help/hurt
your relative performance.
Cautionary note I throw out to those finding very large WWR's: opaque
spandrel glass constructions are not "vertical fenestrations" per the
definitions in 90.1.
Best of luck!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Syed,
Fareed
Sent: Friday, February 18, 2011 3:11 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] how to model 40% glazing on baseline
Hello All,
Can anyone please let me know how to model 40% glass on the baseline
design?
In my proposed design I used customized glass as there is 100% glass on
north and south.
Thanks in advance.
Fareed Syed EIT LEED(r) AP
Analytics Specialist
Halcrow Yolles
One South Dearborn
21st Floor
Chicago, IL 60603
tel: +1 312 212 4430
fax: +1 312 212 4206
www.halcrowyolles.com <http://www.halcrowyolles.com/>
Sustaining and improving the quality of people's lives
Visit our website at http://www.halcrow.com <http://www.halcrow.com/>
------------------------------------------------------------------------
The contents of this email are confidential, for the sole use
of the intended recipient at the email address to which it has
been addressed and do not give rise to any binding legal
obligation upon Halcrow companies unless subsequently confirmed
on headed business notepaper sent by fax, letter or as an email
attachment. Whilst reasonable care has been taken to avoid virus
transmission, no responsibility for viruses is taken and it is
your responsibility to carry out such checks as you feel
appropriate. Emails supplied are as found and there's no
guarantee that the messages contained within the body of the
email have not been edited after receipt. If you receive this
email in error, please contact the sender immediately and delete
the message from your system.
Thank you.
------------------------------------------------------------------------
-
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110221/b1b80c23/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110221/b1b80c23/attachment.jpeg>
More information about the Equest-users
mailing list