[Equest-users] Curve Coefficients
Arpan Bakshi
arpanbakshi at gmail.com
Wed Feb 2 14:16:08 PST 2011
John
You may have already looked over what the 2.1 manual has to offer as far as
explanation on this.
IV.71
H. Calculate the cooling part load ratio.
Some central systems control the operation of the central cooling
coil based upon temperature signals from the zone thermostats
(COOL-CONTROL = WARMEST). Other central systems control the
operation of the central cool ing coil based upon the coil exit
air temperature (COOL-CONTROL = CONSTANT, RESET, or SCHEDULED). In
the latter case, the controller for the cool ing coil has a
throttl ing range. As the temperature of the air leaving the coil
rises and falls within the controller's throttling range, the
controller varies the operation of the coil, increasing or
decreasing the output of the- coil. The action of the controller
must be simulated because it will have an effect on the coil
surface conditions and thus also on moisture removal by the coil.
Because this controller responds to the temperature of the air
stream, the sensible part load ratio of the coil or unit will be
calculated. This value will then be used the following hour to
modify the coil exit air temperature as a function of controller
set point, coil capacity, and controller throttling range
(see DKTEMP algorithm description).
First, the program calculates the total and sensible cool ing
equipment capacities (QCT and QCS)
where
QCT = COOLING-CAPACITY * QCMl (IV.178)
and
QCMl = CVAL(COOL-CAP-FT,EWB,EDB) [COOL-CAP-FT is a correction
function to the total cooling capacity to adjust for off-rated
entering wet-bulb and entering dry-bulb temperatures]
and
QCS = COOL-SH-CAP * QCM2 {however, for direct expansion units, QCS
=
(COOL-SH-CAP * QCM2) + [CONS{l) * CFM * (1.0 - CBF) *
(TM - 80.0)]}
or
QCS = QCT, whichever is smaller,
where
QCM2 = CVAL{COOL-SH-FT,EWB,EDB) [COOL-SH-FT is a correction function,
similar to QCMl, but to the sensible portion of the total
cooling capacity].
The equipment cooling part load ratio (PLRC) and the sensible part
load
ratio «PASTPLRC» are then calculated,
PLRC = QC/QCT
and
<PASTPLRC> = QC - QCLAT / QCS
For direct expansion equipment, the electric power consumed by the
heating
element in the crankcase is calculated as CRANKCASE-HEAT * (1.0 -
PLRC).
2011/2/2 Nick Caton <ncaton at smithboucher.com>
> Hi John,
>
>
>
> To answer your first question… For a DX cooling system, my understanding is
> that COOL-EIR-FT’s temperatures are the outside drybulb (at the
> condenser/heatpump) and the entering wetbulb temperature at the evaporator
> (mixed air conditions). This mirrors how packaged equipment
> efficiencies/capacities are presented in manufacturers’ literature. See
> attached discussion for an example.
>
>
>
> I understand COOL-CAP-FT and COOL-SH-FT curves work from the same
> temperatures.
>
>
>
> To your second question… I’m with you!
>
>
>
> I’d like to see the equation for “hourly electricity consumption” for an
> air-cooled DX process written out in its entirety showing all the affecting
> – I was searching for something analogous to [Volume 2: Dictionary > HVAC
> Components > CHILLER > Chiller Energy Consumption] for airside DX cooling
> systems a while ago and also came up empty-handed. I have a hunch the
> effects of the 3 bypass curves (which are a mystery to me) may have
> something to do with the hourly calculated total capacity and/or EIR though…
> perhaps those need to work their way into your equation?
>
>
>
> Regarding the hourly results you’re using to check your work… I’m not sure
> whether those are the correct figures to work from, but I’d caution to be
> mindful of the wonky effects of altitude on calculated capacities/airflows
> when working with hourly outputs – recent discussion on the list brought
> more to light on this topic – and the effects are more pervasive than I
> originally thought…
>
>
>
> ~Nick
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Grando, John
> *Sent:* Wednesday, February 02, 2011 12:18 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Curve Coefficients
>
>
>
> I'm basically trying to figure out how eQUEST comes up with the total
> Electric consumption for a DX coil. I thought it was the below
>
>
>
> Total Capacity * Capacity Curve [T] * Total EIR * EIR Curve [T] * EIR Curve
> [PLR] but it's not coming out exactly the same. Does anyone have any input
> for what I'm missing. The attached .xls is an example for one day. The
> total capacity is 79.983 kBTU/Hr and the EIR is 0.2722.
>
>
>
>
>
>
>
> *John Grando** **LEED AP**| **Mechanical Engineer
> *Phone: 212-615-3705 | Fax: 212-615-3700
> jgrando at cosentini.com
>
> *Cosentini Associates - A Tetra Tech Company
> *Two Pennsylvania Plaza - Third Floor - New York, NY 10121
> www.cosentini.com
>
>
>
>
>
>
>
>
> NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if any)
> are intended solely for the use of the addressees hereof. In addition, this
> message and the attachments (if any) may contain information that is
> confidential, privileged and exempt from disclosure under applicable law. If
> you are not the intended recipient of this message, you are prohibited from
> reading, disclosing, reproducing, distributing, disseminating or otherwise
> using this transmission. Delivery of this message to any person other than
> the intended recipient is not intended to waive any right or privilege. If
> you have received this message in error, please promptly notify the sender
> by reply E-mail and immediately delete this message from your system.
>
> * *
>
>
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Grando, John
> *Sent:* Wednesday, February 02, 2011 7:55 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Curve Coefficients
>
>
>
> Hello,
>
>
>
> For the curve COOL-EIR-FT the two inputs for a water loop heat pump system
> are "entering wetbulb temperature" and "entering water temperature". I
> understand that the water temperature is the condenser water, but is the
> entering wetbulb temperature for the evaporator side?
>
>
>
>
>
> *John Grando** **LEED AP**| **Mechanical Engineer*
>
>
>
>
>
>
>
>
> NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if any)
> are intended solely for the use of the addressees hereof. In addition, this
> message and the attachments (if any) may contain information that is
> confidential, privileged and exempt from disclosure under applicable law. If
> you are not the intended recipient of this message, you are prohibited from
> reading, disclosing, reproducing, distributing, disseminating or otherwise
> using this transmission. Delivery of this message to any person other than
> the intended recipient is not intended to waive any right or privilege. If
> you have received this message in error, please promptly notify the sender
> by reply E-mail and immediately delete this message from your system.
>
>
>
>
> ---------- Forwarded message ----------
> From: "Nick Caton" <ncaton at smithboucher.com>
> To: "John T. Forester" <JohnTF at BVHis.com>, <
> equest-users at lists.onebuilding.org>
> Date: Wed, 19 Jan 2011 17:43:56 -0600
> Subject: RE: [Equest-users] Air-Cooled EIR Curves
>
> Hi John,
>
>
>
> Hmm… intuitively I think this makes sense, but I haven’t actually gone
> through creating a set of custom packaged DX curves before – lets’ first
> verify we’re looking at the same definition:
>
> Volume 2: Dictionary > HVAC Components > SYSTEM > Cooling Equipment > DX
> Cooling
>
> *COOL-EIR-FT*
>
> Takes the U-name of a bi-linear or bi-quadratic curve that describes the
> Electric Input Ratio for cooling *as a function of entering wet-bulb
> temperature and outdoor dry-bulb temperature (for direct expansion coils)*or entering wet-bulb temperature and entering water temperature for a Water
> Loop Heat Pump (HP) system. At ARI conditions, the value of the curve should
> be 1.
>
> I’m pretty sure the entering wet-bulb is that found entering the evaporator
> coil – the mixed air about to be conditioned. If you check out a typical
> set of packaged DX unit performance tables (If you want a specific example
> to follow along, I’ve just cracked open an engineering guide for the
> Lennox LGH series<http://tech.lennoxintl.com/C03e7o14l/HS7CbNGGFw/ehb_lgh_abox_1010.pdf>*
> to page 21), you’ll find they’ve got OA DB along one axis (85/95/105/115)
> and Entering WB along the other axis (63/67/71). It would appear the same
> tables could also be used to reference data for COOL-CAP-FT and COOL-SH-CAP
> curves.
>
>
>
> Make sense now?
>
>
>
> ‾Nick
>
>
>
> *Disclaimer: I have no particular ties or intent/business to advocate
> Lennox over their competitors – all of their major competitors publish
> similar reference/sizing tables, and this particular unit’s guide just
> happened to be near the top of my reference stack.
>
>
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *John T.
> Forester
> *Sent:* Wednesday, January 19, 2011 4:50 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Air-Cooled EIR Curves
>
>
>
> Quick question,
>
>
>
> When creating custom EIR fT and EIR fPLR curves for air-cooled packaged DX
> units with digital scroll compressors, what are the two independent
> variables? The DOE2 help says to use entering wet-bulb and outside air
> dry-bulb. Where is the entering wet-bulb temperature measured?
> Intuitively, this doesn’t seem correct to me.
>
>
>
> Thanks,
>
>
>
> John
>
>
>
> John T. Forester, P.E., LEED AP, Mechanical Design Engineer *I BVH
> Integrated Services I** *617.658.9008 tel *I** *617.244.3753 fax *I** *One
> Gateway Center Suite 506, Newton MA 02458 *I www.bvhis.com I Hartford ●
> New Haven ● Boston*
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Arpan Bakshi
00 1 646 704-2880
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110202/6ae0f4ea/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110202/6ae0f4ea/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110202/6ae0f4ea/attachment-0001.jpeg>
More information about the Equest-users
mailing list