[Equest-users] U values for fenestrations
Alex Krickx
akrickx at seriousenergy.com
Thu Dec 29 08:43:51 PST 2011
Hi Ali,
I would suggest using WINDOW6 as Nikola suggests. You can vary the size of the window there to match the actual sizes and see what the U-value will be for the window assembly (glass+frame).
In WINDOW6 you can create a "DOE-2 Report" file that has the glass information. This can be imported into eQUEST. Be sure to define your frame-type and frame-width in eQUEST as I don't believe that it will import the frame data from your WINDOW6 report file.
There are other ways to input single U- and SHGC-values for windows, but my understanding is they don't contain the details of angular-dependent transmittance which is important to include.
You should be able to edit the frame conductance in the "Window Properties" Screen in the Detailed Edit mode (below)
[cid:image001.png at 01CCC605.A6441E80]
Regarding your last question about a variety of window sizes - you can create 3 windows in the Wizard mode, and they can be the same glass type of different sizes. If you have more than that, you will need to edit the windows by hand in the detailed mode. I find it easiest to create the correct # of windows first, and then manipulate them to the size I want (rather than creating new window objects in the detailed mode).
Let us know how you do!
Kind regards,
Alex Krickx
Alex Krickx, LEED AP
Building Energy Specialist
Serious Energy, Inc.
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
akrickx at seriousenergy.com
The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments.
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nikola Kravik
Sent: Thursday, December 29, 2011 7:03 AM
To: Ali Murat Tanyer; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] U values for fenestrations
Hi Ali,
You may want to check the Windows 6 program from LBNL on the following link and play with the windows and framing for your checks.
http://windows.lbl.gov/software/window/6/index.html
Best,
Nikola
Nikola Kravik, LEED AP
Project Engineer
Willdan Energy Solutions
11875 Dublin Boulevard, Suite A-201
Dublin, California 94568
T. 925.556.2600 ext. 1228
C. 925.719.5883
F. 925.556.1444
nkravik at willdan.com
www.willdan.com/energy
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ali Murat Tanyer
Sent: Thursday, December 29, 2011 5:32 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] U values for fenestrations
Dear all,
I am trying to understand the best way to enter the U value of my
fenestrations as a whole system. The manufacturer specified the U value
of the glazing as 0.49 BTU/hr·ft2°F and the aluminium framing as 0.70
BTU/hr·ft2°F. I do not have the NFRC data of my fenestration.
I can enter the properties of the glazing however I couldn't find a way
to define the thermal properties of the aluminium framing. I have also
checked the detailed mode screens.
The dimensions of the fenestration varies in different locations. So
what is the best way to calculate and enter the U-factor for the overall
fenestration area (including glazing and framing)?
My aim is making my simulation as accurate as possible since I want to
compare the results with actual values.
Thanks in advance.
Ali
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111229/5aced252/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 23637 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20111229/5aced252/attachment.png>
More information about the Equest-users
mailing list