[Equest-users] Chillers in Series inputs
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Sat Apr 23 10:28:14 PDT 2011
Hmmmm---I wasn't aware or didn't see this specifically myself---- can you
show me a screen shot where you are seeing this in eQuest?
I will have to dig deeper....
Thanks,
Pasha
On Fri, Apr 22, 2011 at 2:55 PM, Anthony Hardman
<Anthony at greenengineer.com>wrote:
> The keyword “SERIES-SETPT-RAT“ to setup chillers in series is still
> listed as future in the help files. Could that be why you’re running into
> trouble?
>
> * *
>
> *Anthony Hardman, PE*
>
> *LEED AP BD&C***
>
> Building Performance Analyst
>
>
>
> *THE GREEN ENGINEER, LLP***
>
> *Sustainable Design Consulting – Energy Modeling – LEED Project Management
> *
>
> 50 Beharrell St
>
> Concord, MA 01742
>
> O: 978/610-2801
>
> C: 720/840-7862
>
> www.GreenEngineer.com <http://www.greenengineer.com/>
>
> www.linkedin.com/in/ahardman81
>
> http://twitter.com/#!/a_Hardman
>
>
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Pasha
> Korber-Gonzalez
> *Sent:* Friday, April 22, 2011 2:04 PM
> *To:* James Hansen
>
> *Cc:* eQUEST Users List; Arunabha Sau
> *Subject:* Re: [Equest-users] Chillers in Series inputs
>
>
>
> Thanks Rob & James for your prompt input to my dilemma....after I sent the
> email to the list, I went back in my plants to try and make sense why the
> secondary wasn't seeing a load--so for a random test I switched the
> assignement of the two chillers (just reversed which loops they are on.) and
> then ran the sim without errors. That was the good news. I don't have my
> head around the logic of why that worked on the first try, but maybe I was
> having some dislexia-input moments and spec'd my chiller conditions
> backwards (i.e. high chiller & low chiller in the series).
>
>
>
> Since it has ran I noticed an immediate reduction in chiller energy use,
> but I haven't yet verified if the reduction is realistic and if there are
> any other QC error type things to verify that this approach is indeed
> modeling the chiller temps in series. I don't think I will mess with
> custom chiller curves at this point because this project model is only SD.
> Therefore I won't be held to any compliance reviews and strict performance
> results...at least not at this point in time.
>
>
>
> I'll try to send feedback when I can verify that this is a valid input
> option for chillers in series, or if it holds no water at all...
>
>
>
> Cheers,
>
> Pasha
>
> On Fri, Apr 22, 2011 at 12:18 PM, James Hansen <JHANSEN at ghtltd.com> wrote:
>
> Most manufacturers will give you a “single chiller” performance curve for
> the two chillers in series. I typically just make custom chiller curves to
> represent series chillers as a single chiller. If a designer creates
> valving that allows water to NOT have to flow through both chillers during
> low load operation, this gets a little tricky, and I end up averaging the
> delta P across the chillers to represent partial operation thru both
> chillers and partial operation thru a single chiller. No easy way to do
> this.
>
>
>
> *GHT Limited
> **James Hansen, PE, LEED AP*
>
> *Senior Associate*
>
> 1010 N. Glebe Rd, Suite 200
>
> Arlington, VA 22201-4749
>
> 703-338-5754 (Cell)
>
> 703-243-1200 (Office)
>
> 703-276-1376 (Fax)
>
> www.ghtltd.com
>
> * *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Rob Hudson
> *Sent:* Friday, April 22, 2011 2:15 PM
> *To:* Pasha Korber-Gonzalez
> *Cc:* eQUEST Users List; Arunabha Sau
> *Subject:* Re: [Equest-users] Chillers in Series inputs
>
>
>
> I won't claim that this is correct whatsoever, but briefly looking at your
> set up, it is clear that the water isn't pulling extra load from the second
> chiller. I think you may want to set up a single chiller because I don't
> see a way to get the water to go through both chillers. You could also
> create your own custom curves so that you match the combined performance of
> the modeled chiller.
>
>
>
> Just a thought.
>
>
>
> Rob
>
> On Fri, Apr 22, 2011 at 1:55 PM, Pasha Korber-Gonzalez <
> pasha.pkconsulting at gmail.com> wrote:
>
> Hi,
>
>
>
> I could use some guidance to make sure I'm assuming the correct inputs to
> set up chillers in series. This is the first time I'm trying to model this
> and I have it set up with a primary & secondary loop for a total delta T of
> 16 across 2 chillers. I'm getting a run error of the secondary loop
> having NO DESIGN FLOW/LOAD, but I'm not sure how to show that load on the
> secondary loop.....maybe I have the chillers listed backwards???
>
>
>
> Can anyone take a quick look at the setup in the Plant Module and let me
> know what I am missing on this? I couldn't find any info on chillers in
> series in the DOE-2 docs to guide me on the correct inputs and setup.
>
>
>
> .pd2 & inp files attached.
>
>
>
> Thanks in advance for your keen eye and guidance on my model.
>
>
>
> Pasha
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
> --
> Rob Hudson
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110423/992dbcbc/attachment.htm>
More information about the Equest-users
mailing list