[Equest-users] Min Flow Rate below Min OA
Molly Curtz
molly.curtz at arup.com
Thu Apr 21 15:14:35 PDT 2011
Neil,
There's not a hassle-free way to fix this. In order to avoid the behavior you're seeing, you can specify the min flow ratio for each zone at the zone level (rather than at the system level). In this case, you will need to manually verify that the zone OA requirement is less than the min flow ratio you input for each zone. If the zone OA requirement dictates the zone minimum flow, then leave the min flow ratio blank for that zone (to avoid reducing flow below the min OA requirement.)
The Advanced VAV Design Guide includes more guidance on using eQuest to model VAV system control sequences:
http://www.energydesignresources.com/resources/publications/design-guidelines/design-guidelines-advanced-variable-air-volume-(vav)-systems.aspx
Kind regards,
Molly
Molly Curtz
Mechanical Engineer
Arup
403 Columbia Street Suite 220 Seattle WA 98104
t +1 206 749 9674 d +1 206 493 2234
f +1 206 749 0665
www.arup.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Neil Patel
Sent: Monday, April 18, 2011 6:04 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Min Flow Rate below Min OA
Hello,
I am modeling a VAV system and I am entering either Min-OA/person or Min-OA/area for each zone. I ran an hourly report and noticed that when I specify a minimum flow ratio the system flow rate will drop below the minimum OA rate.
Has anyone had this issue and is there a way to get the flow to stay above the ventilation requirement?
Thanks in advance,
Neil Patel, EIT, LEED AP BD+C
[cid:image001.jpg at 01CC0036.D02B3BB0]
EME Group | Consulting Engineers, LLC
159 West 25th Street, 5th Floor
New York, NY 10001
Tel: 212-529-5969
Fax: 212-529-6023
www.emegroup.com<http://www.emegroup.com>
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110421/bd8894ba/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1822 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110421/bd8894ba/attachment.jpg>
More information about the Equest-users
mailing list