Tai,
I generally model mechanical/electrical spaces separately from
conditioned spaces, but I combine mechanical and electrical spaces into
one zone when they are adjacent to each other. I usually model
vestibules as separate zones, since they tend to have their own cabinet
unit heaters to handle the infiltration and envelope loads. I often
combine interior zones with little or no load (such as storage rooms)
with adjacent zones. I combine janitor closets with adjacent corridors
if that is where they pull their outside air from. Sometimes I do that
with bathrooms as well but then the space-by-space lighting density
(from Table 9.6.1, ASHRAE 90.1) gets trickier.
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
wbishop at pathfinder-ea.com <mailto:wbishop at pathfinder-ea.com>
www.pathfinder-ea.com <http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Tai
Lieu
Sent: Wednesday, April 20, 2011 5:02 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Zoning Odd Spaces - Designing for LEED Canada NC
1.0MNECB
Hello All,
I've been searching constantly on google through the old responses for
Zoning spaces, before i got to the 6th keyword I called it quits and
decided
to personally ask the eQuest community for your knowledge.
I'm working on a building using thats 200,000 sq-ft heat pumps
What do you guys generally do with mechanical, electrical, vestibule
spaces?
What I intended on doing with the mechanical spaces is to model them as
unconditioned
OR simplify the model more by grouping them in with the larger spaces
BUT there's a fair amount of them for the heat pumps.
Let me know what you're opinion is?
Tai Lieu
LEED AP BD+C
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110420/ccaa87d5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110420/ccaa87d5/attachment.jpeg>
More information about the Equest-users
mailing list