[Equest-users] Where to find summary of overridden defaults etc.
Carol Gardner
cmg750 at gmail.com
Wed Apr 20 13:00:18 PDT 2011
Just a couple of comments, Mark. If a default was overridden, it would be
you who did it so you would know what you overrode it with. If I am
misunderstanding and you just couldn't see what the default was you can view
it, usually by right clicking on the input box.
I am curious why the reviewer asked that autosizing not be done for the
baseline. I was reading my Std 90 2004 User's guide this morning and was
kind of surprised that in it they more or less suggest you need to oversize
by hand. I'm not sure why. I know that you need to be careful where you put
the 15% and 25% sizing increases in eQUEST but it's relatively easy to get
them in the right spot.
As a check let me know what you think of my methodology. I set the system
sizing ratio on the first screen of the Air-Side HVAC System to 1.0, and
then set the Cool Size Ratio to 1.15 on the first screen under the Cooling
tab, and the Heat Size Ratio to 1.25 of the first screen under the Heating
tab. Is this what others do?
Carol
On Wed, Apr 20, 2011 at 11:15 AM, Mark Darrall <MDarrall at a2so4.com> wrote:
> Thanks, everyone!
>
>
>
> Don’t forget, too, that the Appendix G requirements don’t always jive with
> default eQ values. Also, my reviewer has asked that autosizing not be done
> for baseline, which probably meant more overrides…
>
>
>
> I appreciate the tip on searching the .inp file. Thanks!
>
>
>
> MARK DARRALL, AIA, LEED AP BD+C, NCARB
> Senior Project Manager
>
>
>
> [image: a2so4-email]
>
>
>
> DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
>
>
>
> A2SO4 Architecture, LLC
>
> Union Station
> 300 South Meridian Street / 250
> Indianapolis, Indiana 46225
> TEL 317 388 8850
>
> FAX 317 280 0692
>
> MOB 765 749 0841
> www.a2so4.com
>
>
>
> *Please consider the environment before printing this e-mail*.
>
>
>
> CONFIDENTIALITY NOTICE: This email and any files transmitted with it are
> confidential and intended solely for the use of the individual or entity to
> which they are addressed. If you are not the intended recipient, you may not
> review, copy or distribute this message. If you have received this email in
> error, please notify the sender immediately and delete the original message.
> Neither the sender nor the company for which he or she works accepts any
> liability for any damage caused by any virus transmitted by this email.
>
>
>
> *From:* R B [mailto:slv3sat at gmail.com]
> *Sent:* Wednesday, April 20, 2011 1:12 PM
> *To:* Nick Caton
> *Cc:* Mark Darrall; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Where to find summary of overridden defaults
> etc.
>
>
>
> If in the baseline (and may be the proposed case), I have made changes from
> the auto-sizing (and from the proposed design) to reduce the unmet hours, I
> count that as default over-ridden. This is usually a small number (less than
> 5 if I remember correctly).
>
> On Wed, Apr 20, 2011 at 11:36 AM, Nick Caton <ncaton at smithboucher.com>
> wrote:
>
> Hi Mark,
>
>
>
> For eQuest, I don’t believe there is any reasonable way to tally “default
> overrides.” For LEED submittals, I typically enter zeroes at the
> corresponding template queries, and that’s what I’ve suggested to others for
> initial submittals. I’ve heard others enter “9999” in all fields without
> comment, but 0 seems less conspicuous to me =).
>
>
>
> There’s further discussion on this topic in the archives –
> bookmark/favorite these links if you haven’t already:
>
> http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/
>
> http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/
>
>
>
> If a reviewer were to push me to come up with a figure without any specific
> guidance after an initial submittal, I suppose I would paste the .inp file
> into a word document, ctrl+f for instances of the text “..” without quotes,
> and explain that number represents an estimate of the number of non-library
> entries in the project (screengrab):
>
> I would probably wonder about the reviewer somewhere along the way too...
> Anyone familiar with eQuest and LEED knows there’s no way to finish a
> 90.1-based model without a horde of non-default entries… I’m having
> difficulty guessing at how this figure could help an eQuest model reviewer
> do their job properly. Perhaps it’s specific to other software packages…
> Thoughts anyone?
>
>
>
> To be clear, I’d sooner advise just entering 0’s in lieu of jumping through
> any unnecessary hoops.
>
>
>
> ~Nick
>
>
>
> [image: cid:489575314 at 22072009-0ABB]
>
> * *
>
> *NICK CATON, E.I.T.*
>
> PROJECT ENGINEER
>
> Smith & Boucher Engineers
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Mark Darrall
> *Sent:* Wednesday, April 20, 2011 10:11 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Where to find summary of overridden defaults
> etc.
>
>
>
> Hi,
>
>
>
> I know that when a run has issues, it creates an ATTN report with the
> warnings listed. But how can I find out how many default values have been
> overridden without going through every screen and counting them?
>
>
>
> Thanks, all!
>
>
>
> MARK DARRALL, AIA, LEED AP BD+C, NCARB
> Senior Project Manager
>
>
>
> [image: a2so4-email]
>
>
>
> DESIGN ENRICHING LIFE // LIFE ENRICHING DESIGN
>
>
>
> A2SO4 Architecture, LLC
>
> Union Station
> 300 South Meridian Street / 250
> Indianapolis, Indiana 46225
> TEL 317 388 8850
>
> FAX 317 280 0692
>
> MOB 765 749 0841
> www.a2so4.com
>
>
>
> *Please consider the environment before printing this e-mail*.
>
>
>
> CONFIDENTIALITY NOTICE: This email and any files transmitted with it are
> confidential and intended solely for the use of the individual or entity to
> which they are addressed. If you are not the intended recipient, you may not
> review, copy or distribute this message. If you have received this email in
> error, please notify the sender immediately and delete the original message.
> Neither the sender nor the company for which he or she works accepts any
> liability for any damage caused by any virus transmitted by this email.
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110420/9c2c6640/attachment.htm>
More information about the Equest-users
mailing list