[Equest-users] parametric run
Bishop, Bill
wbishop at pathfinder-ea.com
Tue Apr 19 07:37:55 PDT 2011
Vipin,
When I model cool roofs for ASHRAE Standard 90.1 Appendix G, I change
the absorptance of the roof construction to 0.55, per the
reflectance=0.45 allowance in Table G3.1.
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
wbishop at pathfinder-ea.com <mailto:wbishop at pathfinder-ea.com>
www.pathfinder-ea.com <http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vipin
Sharma
Sent: Monday, April 18, 2011 7:14 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] parametric run
Hi....................
How parametric run is done in eQUEST. I am
beginner .Can anyone tell me
for cool roof parametric run.Thanks in advance.
Regards
vipin sharma
student
Energy Engg.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110419/45e461f7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110419/45e461f7/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 36845 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110419/45e461f7/attachment-0001.jpeg>
More information about the Equest-users
mailing list