[Equest-users] No Roof Conduction Load

David Eldridge dse at grummanbutkus.com
Mon Apr 18 18:45:25 PDT 2011


Your peak load components should be coming into the ceiling of the
conditioned room below the plenum.  You can check this by changing the
roof insulation and seeing what happens to the ceiling load component.

David



-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Derek W
Kultgen
Sent: Monday, April 18, 2011 8:26 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] No Roof Conduction Load

Hello all:

For some reason on the peak load components output eQuest reads that none
of the load contribution is from roof conduction. It is unconditioned
space but I should still be getting a significant load coming from the
roof. I didn't set it to adiabatic and the insulation in the attic is only
R19. Has anyone experienced this before?

Any help is greatly appreciated.

Thanks,
Derek Kultgen
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG


More information about the Equest-users mailing list