[Equest-users] How to Model Infiltration based on Pressure
David Reddy
david.j.reddy1 at gmail.com
Wed Apr 13 10:28:38 PDT 2011
Steve-
Here is a link to a paper published by PNNL discussing some guidelines
for converting building leakage rates at a known pressure to energy
model infiltration inputs.
http://www.pnl.gov/main/publications/external/technical_reports/PNNL-18898.pdf
It is written in the context of EnergyPlus, but eQUEST/DOE-2 includes
the same infiltration model (AIR-CHANGE -> AIR-CHANGES/HR). In my
experience using this guideline, you'll have to do some calculations of
exterior wall area and perimeter zone floor area to come up with the
correct infiltration inputs for each SPACE; keyword defaulting can come
in handy for this task... Also, this guideline doesn't go into depth on
how to develop infiltration schedules that reflect the design capacity
and control of different types of ventilation systems. Rather from what
I gleaned, the guideline is simply 1.0 when fans are off, and 0.25 when
fans are on. Finally, keep in mind that DOE-2 calculates a local wind
speed from weather file wind speed and SITE-PARAMETER inputs that
describe characteristics of both the weather station and the terrain
local to the building. These parameters (which I overlooked until
researching these infiltration models), do have an impact on the
calculation of hourly SPACE loads, since the local wind speed
calculation not impacts the wind-dependent infiltration model, but also
exterior (wall and window) film conductance.
The authors acknowledges that the recommended model addresses only
"wind-driven" infiltration, so if stack-driven flow is a major component
in your building, you may want to figure out a way to adjust your
inputs/schedules to account for this; a combination of AIR-CHANGES/HR
and the other model input, INF-FLOW/AREA, could be one approach for
dealing with this. The DOE-2 Crack model does attempt to account for
stack driven flow, but this model is sensitive to it's many,
component-specific inputs, which are often difficult to characterize.
-David
--
David Reddy
360 Analytics
Building Energy Analysis Consultants
mail: 12354 16th Ave NE, Seattle, WA 98125
office: 206.420.7918
mobile: 206.406.9856
web: www.360-Analytics.com
On 4/13/2011 5:39 AM, Steve Burley wrote:
>
> As part of the Estidama, the local ABU Dhabi requirements, we are
> required to model "building air leakage rates" on 2l/s/m² at 75Pa. Is
> it possible to model this in equest? The help file would suggest so if
> AIR-CHANGES/HR is used but this is corrected for wind speed.
>
> Are the corrections held in the P-Inf and C-Inf (perimeter and core
> infiltration?) schedules or are they calculated during the simulation run?
>
> Any help would be gratefully received.
>
> Regards,
>
> Steve
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG