[Equest-users] 90.1 Supply Fan Energy
Paul Diglio
paul.diglio at sbcglobal.net
Wed Apr 6 14:50:44 PDT 2011
Michael:
Just out of curiosity, what did you calculate for the kW/CFM?
I have modeled buildings where the ventilation fans use much more energy than
the heating and cooling energy combined.
Paul Diglio
________________________________
From: Carol Gardner <cmg750 at gmail.com>
To: M. Shields <mshields at fstrategies.com>
Cc: equest-users at lists.onebuilding.org
Sent: Wed, April 6, 2011 5:46:30 PM
Subject: Re: [Equest-users] 90.1 Supply Fan Energy
Yes, that is correct and obviously there isn't a large number in there. The
default is 0.5 cfm/sf. I really think it's your outdoor air. Try changing it to
cfm/person.
On Wed, Apr 6, 2011 at 1:47 PM, M. Shields <mshields at fstrategies.com> wrote:
Do you mean under the Systems->Fans->Flow Parameters Min Flow cfm/ft2? I left
this blank thinking that equest would then size the flow rate based on my design
parameters for supply air temp and zone temp as Appendix G requires, is that
incorrect?
>
>From:Carol Gardner [mailto:cmg750 at gmail.com]
>Sent: Wednesday, April 06, 2011 4:04 PM
>
>To: M. Shields
>Cc: equest-users at lists.onebuilding.org
>Subject: Re: [Equest-users] 90.1 Supply Fan Energy
>
>Under the HVAC systems tab, go to the Air Flow screen and look for the field
>labeled cfm/sf. It usually defaults to 0.5 cfm/sf, something I've been going on
>about a bit lately on this listserv. A better number is 1 or so, usually but it
>depends on building type, exposure, etc. For you, make sure it is not too large.
>I suspect, however, that this is not where your problem is. I suspect you have
>accidentally entered too much OA. I suggest you go back and simply put in the
>Standard 62 cfm/person rate and call it good. I have never specified it as a cfm
>rate but that sounds like not such a good idea for energy modeling. See if that
>helps.
>On Wed, Apr 6, 2011 at 12:57 PM, M. Shields <mshields at fstrategies.com> wrote:
>I looked at the ACH based on the SV-A system CFM and the volume of the zone and
>it does seem high (2-5 ACH), but I let equest calculate the system CFM for me.
>
>I have one system per zone so I specified OA in the zone tab as a overall CFM
>rate based on the 62.1 calculations I did.
>
>From:Carol Gardner [mailto:cmg750 at gmail.com]
>Sent: Wednesday, April 06, 2011 3:37 PM
>To: M. Shields
>Cc: equest-users at lists.onebuilding.org
>Subject: Re: [Equest-users] 90.1 Supply Fan Energy
>
>Check your cfm/sf number in your systems, that would definitely cause this if
>it's set too high. Also what field are you using for your OA ventilaton?
>
>
>Carol
>On Wed, Apr 6, 2011 at 12:22 PM, M. Shields <mshields at fstrategies.com> wrote:
>Hi all,
>
>I am in the process of breaking out the fan energy from my HVAC system per
>ASHRAE 2004 G3.1.2.1, following G3.1.2.9. The amount of energy coming from my
>fans seems massive and I’m not sure if that is typical, or if I’ve messed
>something up. I started by setting the temperature difference of 20 degrees
>between supply and desired temp (55/75 cooling and 90/70 for heating) and
>specified 62.1-2004 ventilation for outside air. I then ran equest and used the
>SV-A reports to get supply CFM for each system. From that number I then used
>Table G3.1.2.9 to get BHP for each system, which I then converted to kW using
>the formula in ASHRAE. I then took that number and divided by CFM to get kw/CFM
>and entered this number on the system->fan tab. When I go to the SV-A report
>the system kW is exactly what I calculated it to be, but the energy required for
>my ventilation fans is about the same as my heating and cooling load combined,
>which seems outrageous.
>
>
>Is this typical? Have I entered it In the wrong way? I would think fan
>consumption would typically be a fraction of the actually heating and cooling
>energy. Thanks for any thoughts.
>
>____________________________
>Michael Shields
>Facility Strategies Group, LLC
>1012 Market Street, Suite 307
>Fort Mill, SC 29708
>Phone: 803-493-4507
>Fax: 803-548-2511
>Email: mshields at fstrategies.com
>
>
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>--
>Carol Gardner PE
>
>
>
>--
>Carol Gardner PE
>_______________________________________________
>Equest-users mailing list
>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Carol Gardner PE