[Equest-users] Outside Air Supply
Carol Gardner
cmg750 at gmail.com
Tue Apr 5 10:50:51 PDT 2011
Go into your Project and Site tab and set your altitude to 0. For an
explanation of this search the archives.
On Tue, Apr 5, 2011 at 10:01 AM, M. Shields <mshields at fstrategies.com>wrote:
> Hi all,
>
>
>
> I am trying to set up a model to which uses minimum ASHRAE 62.1 ventilation
> rates and I’m having a bit of trouble. My understanding is that in the zone
> setup the outdoor air can be setup to use 4 different specification methods,
> but equest will only use whichever is greatest (ie, 5cfm/person or .06
> cfm/sqft) but not combine them. It therefore seems like the best method for
> this is to use 62.1 to calculate cfm/zone and just enter that number.
>
>
>
> I then go to my system screen for OA, where I can specify the OA ratio,
> control method, etc. If I set the ratio to be 1, and the sizing method to
> be Sum of Zone OA , then when I go to the SV-A report shouldn’t my numbers
> there match exactly what I have entered for all my design values? I set up
> a very simple zone that had 100 cfm design flow, 50 cfm min OA, and 50 cfm
> exhaust, and then when I run a simulation and open the SV-A report it lists
> my design cfm as 103, OA as 52, and exhaust as 53. I don’t understand why
> these design values are slightly higher, anyone have any thoughts?
>
>
>
> ____________________________
> Michael Shields, EIT
> Facility Strategies Group, LLC
>
> 1012 Market Street, Suite 307
>
> Fort Mill, SC 29708
>
> Phone: 803-493-4507
>
> Fax: 803-548-2511
> Email: mshields at fstrategies.com
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110405/c695455f/attachment.htm>
More information about the Equest-users
mailing list