[Equest-users] Aircraft Hanger Modeling
Arpan Bakshi
arpanbakshi at gmail.com
Mon Apr 4 13:09:35 PDT 2011
Have you looked into using the natural ventilation option with either air
change or sherman-grimsrud method?
Switch to Detailed Mode > Air-Side HVAC > Outside Air > Natural Ventilation
On Mon, Apr 4, 2011 at 3:57 PM, nabil koubaa <nkoubaa at gmail.com> wrote:
> thank you for your help Matthew this is great information exactly what I
> was looking for.
>
>
> On Mon, Apr 4, 2011 at 3:54 PM, <MatthewRLarson at eaton.com> wrote:
>
>> If you go to the hangar space properties under Internal Loads and the
>> Infiltration tab, you can apply an hourly schedule there. Below is a screen
>> shot of the infiltration tab and the help file for the Schedule. I believe
>> this has to be done in detailed mode, not wizard mode. Let me know if you
>> want to see an example schedule or something.
>>
>>
>>
>> [image: cid:image002.jpg at 01CBF2CF.97AF6F00]
>>
>>
>>
>> Thanks,
>>
>>
>>
>> *Matthew Larson, LEED AP BD+C
>> *Project Engineer
>>
>> Energy Solutions Group**
>>
>> E M C Engineers, Inc.
>> Eaton’s Electrical Services & Systems
>> 143 Union Blvd, Suite 350
>> Lakewood, CO 80228
>> tel: +1 303 328-3419
>> mobile: +1 303 668-2511
>> fax: +1 303 974-1239
>>
>> MatthewRLarson at Eaton.com
>> www.eaton.com/energysolutions
>>
>> [image: image001]
>>
>>
>>
>> *From:* nabil koubaa [mailto:nkoubaa at gmail.com]
>> *Sent:* Monday, April 04, 2011 1:47 PM
>> *To:* Larson, Matthew R
>> *Cc:* equest-users at lists.onebuilding.org
>> *Subject:* Re: [Equest-users] Aircraft Hanger Modeling
>>
>>
>>
>> Matthew,
>>
>> using the infiltration could be the way to go, I know that it is possible
>> to create a parametric run for infiltration but is it possible to put it on
>> a schedule?
>>
>> thank you
>>
>>
>>
>> On Mon, Apr 4, 2011 at 3:38 PM, <MatthewRLarson at eaton.com> wrote:
>>
>> Just a thought, but could you treat it as infiltration. Under Internal
>> Loads, specify a high infiltration rate and create an infiltration schedule
>> based on hangar doors opening and closing at different times during the
>> day. If anyone has any other ideas, please share.
>>
>>
>>
>> Thanks,
>>
>>
>>
>> *Matthew Larson, LEED AP BD+C
>> *Project Engineer
>>
>> Energy Solutions Group
>>
>> E M C Engineers, Inc.
>> Eaton’s Electrical Services & Systems
>> 143 Union Blvd, Suite 350
>> Lakewood, CO 80228
>> tel: +1 303 328-3419
>> mobile: +1 303 668-2511
>> fax: +1 303 974-1239
>>
>> MatthewRLarson at Eaton.com
>> www.eaton.com/energysolutions
>>
>> [image: image001]
>>
>>
>>
>> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
>> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *nabil koubaa
>> *Sent:* Monday, April 04, 2011 12:20 PM
>> *To:* equest-users at lists.onebuilding.org
>> *Subject:* [Equest-users] Aircraft Hanger Modeling
>>
>>
>>
>> Hello all-
>>
>> I'm modeling an aircraft hanger and I'm not sure how to model hanger doors
>> being opened and closed at different times per day.
>>
>>
>>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
*
*
*
Arpan Bakshi LEED AP BD+C
*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110404/b2ddca87/attachment.htm>
More information about the Equest-users
mailing list