[Equest-users] Absorption Chiller Power Use
Bishop, Bill
wbishop at pathfinder-ea.com
Fri Apr 1 11:38:09 PDT 2011
Cory,
Make sure you enter the chiller capacity correctly. 4 tons = 48,000
Btu/h = 0.048 MBtu/h in eQUEST (not 48 MBtu/h).
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
wbishop at pathfinder-ea.com www.pathfinder-ea.com
<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Cory
Duggin
Sent: Friday, April 01, 2011 2:04 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Absorption Chiller Power Use
My absorption chiller model is using way more power for pumping than it
should be. How can I reduce their usage? I feel like the model is
trying to use a pump that is too large for the capacity of my chiller
which is about 4 tons. Thanks
--
Cory Duggin, EI
Tennessee Tech University
Graduate Research Assistant
Mechanical Engineering
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110401/d6743759/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2412 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110401/d6743759/attachment.jpeg>
More information about the Equest-users
mailing list