[Equest-users] FW: Custom curves - Loop to Loop Heat Pump
Ana N.
ananeddav at hotmail.com
Thu Sep 30 06:58:06 PDT 2010
Carol,
DOE22Vol2-Dictionary_47b, pages 220-221 indicate that only one curve should be used. That is why I tried creating only one curve. I assume we should create one curve EIR= t ( t evaporator leaving, t cond entering). It is relatively simple for the cooling mode. In the heating mode, the evaporator leaving temperature is actually the source fluid leaving temperature (manufacturers typically provide the data for the source fluid entering temperature), while the condenser entering temperature would be the load fluid entering temperature (manufactures typically provide the data for the load fluid leaving temperature). Do you agree with this rationale? Unfortunately, I do not like much the results I got.
DOE22Vol2-Dictionary says that curves should be normalized at the Eurovent rating condition, rather than ARI.
Thank you
Ana
Date: Wed, 29 Sep 2010 18:49:39 -0700
Subject: Re: [Equest-users] FW: Custom curves - Loop to Loop Heat Pump
From: cmg750 at gmail.com
To: ananeddav at hotmail.com
CC: equest-users at lists.onebuilding.org
Hi Ana,
As always it would be good to see what you are looking at so if you feel comfortable sending your .inp and .pd2 files please do. I'm not sure why the HIR field is grayed out but I can understand why 2 HIR curves would confuse eQUEST. You will have to do a parametric run or just run your model twice, once with one curve and again with the other curve. Also, be sure to read the information about curves and curve inputs in the DOE2 manual. All the data needs to be normalized around the ARI conditions and the ARI conditions always equal 1.0. It can be confusing at first.
Good luck!
Carol
On Wed, Sep 29, 2010 at 2:29 PM, Ana N. <ananeddav at hotmail.com> wrote:
Dear e-quest users,
I am modeling a central ground source heat pump that provides both cooling and heating by using the Loop to Loop Heat Pump. I am trying to derive the performance curves based on a very detailed set of data provided by the manufacturer. What confuses me is that HIR field under the performance curve tab is grayed out.
I have derived one curve by combining the performance data for cooling and heating mode (by using methodology described for chillers, “Tools and Techniques to Calibrate Electric Chiller Component Models, ASHRAE Symposium” ). I am not sure this is the correct approach. Should I create one EIR curve by combining the data for cooling and heating (EIR= f(T evaporator leaving, T cond entering) and leave HIR curve “grayed out”?
I also run the model with two separate curves
EIR= f (T evaporator leaving, T cond entering),
HIR= f(T evaporator leaving, T cond entering),
each derived using the performance data for corresponding mode of operation.
However, when I run the model with two different HIR curves, the result remains unchanged as if e-quest does not use this curve at all.
At this point, I am using default EIR=f( part load). I am still using e-quest 3-63.
I would really appreciate sharing your experience in modeling the Loop to Loop Heat Pump and deriving custom curves.
Thank you
Ana
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100930/972da37d/attachment.htm>
More information about the Equest-users
mailing list