[Equest-users] Condenser Water Storage

David Bastow dbastow at mcclure-engineering.com
Tue Sep 28 09:16:56 PDT 2010


We have modeled in eQUEST an existing large office building that had
chiller/heat pumps with evaporative cooling towers, where we had a hot
water loop with hot thermal storage heated by the heat pump with boiler
back up.  The hot water loop was typically like 95 degrees.  We also had
a chilled water loop that had cold thermal storage.  The separate
cooling tower loop was able to cool the chilled water loop when cooling
tower loop temperatures allowed it.  The chilled water loop was
typically like 50 degrees.  We had around 250,000 gallons of existing
underground thermal storage tanks on the project.  Our building thermal
storage had 4 tanks with the valving capability of us switching from
100% hot thermal storage to 100% chilled water storage and anywhere in
between at 25% levels, at different times of the year.    
 
When we first set out to do this eQUEST model we were not sure from
documentation that eQUEST could model it.  Due to the fact that we could
not fail, and delay the project, and lose time having to start over
modeling in another program, we did two concurrent models one with
eQUEST and one with Micro-AXCESS.  I did the Micro-AXCESS model and
another gentleman in our firm did the eQUEST model.  Micro-AXCESS is a
DOS based hourly climate history based energy modeling program that we
had used for over 17 years, that we had modeled projects of this type in
earlier and we knew it would model it for sure.  We compared the output
results of both programs and they were very similar. 
 
In the end both programs, for this particular site showed, that due to
additional losses with the storage tanks,etc., that we used slightly
more energy with the storage tanks than without and for this Northern
USA site the operating costs were higher.  This may not be true with a
different climate site location.  Also, our site did not have lower
electrical rates at night, that might be a consideration at other
locations.
 
I have attached some info from the eQUEST item helps on the subject to
take a look at.
 
David A. Bastow 
McClure Engineering, Inc.  

________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Cassie
Waddell
Sent: Monday, September 27, 2010 5:25 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Condenser Water Storage



Has anyone ever attempted to model condenser water storage using eQuest?
The idea is to run the cooling towers at night to take advantage of the
low WB temps and then use condenser water directly in a radiant system
instead of running the chillers. It looks to me like the only way to
model thermal storage is on the chilled water loop. 

 

Please let me know if you have any ideas. Thanks,

 

 

 

Cassie Waddell  P.E.  LEED AP

Mechanical Engineer

 

Arup

560 Mission Street  Suite 700  San Francisco  CA 94105

t +1 415 957 9445  d +1 415 946 1660

f +1 415 957 9096  

www.arup.com <http://www.arup.com>  

 

____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100928/dc1d9326/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Thermal Storage Helps.pdf
Type: application/octet-stream
Size: 310230 bytes
Desc: Thermal Storage Helps.pdf
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100928/dc1d9326/attachment.obj>


More information about the Equest-users mailing list