[Equest-users] Entering Unmet hours in LEED Online
Nick Caton
ncaton at smithboucher.com
Wed Sep 22 10:22:25 PDT 2010
Quickly, the answer is your last suggestion: multiply BEPS % by the 'hours fans on.'
This does not break apart the heating and cooling figures, so you must extrapolate in a manner you're comfy with to weight between the two. I reference the zone reports to do this weighting.
Carol's making a good point that will doubtless save you time in the future... Any eQuest user should have the following archive search sites bookmarked in their browser:
- http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/ <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/> (tip: search for my name and the word 'coincidental' for some suggested write-ups on your question)
- http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/ <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/>
These archives are a primary resource when you have eQuest-specific questions, and you can basically get an instant response if your question has already been discussed ;).
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Carol Gardner
Sent: Wednesday, September 22, 2010 11:35 AM
To: Omar Katanani
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Entering Unmet hours in LEED Online
There was an in depth discussion of this not too long ago. Look for that thread and if you still have questions email us again.
Carol
On Wed, Sep 22, 2010 at 9:05 AM, Omar Katanani <omar at ecoconsulting.net> wrote:
Dear all,
When submitting the LEED Online templates, I am asked to enter the:
a. Number of hrs heating loads not met
b. Number of hrs cooling loads not met
Are these the same as the BEPS report's "HOURS ANY ZONE ABOVE COOLING THROTTLING RANGE" and "HOURS ANY ZONE BELOW HEATING THROTTLING RANGE" ?
OR
Shall I add the hours of each month of every zone (the last 2 columns of SS-F Zone Demand Summary for each zone)? (HOURS UNDERHEATED & HOURS UNDERCOOLED)
Accordingly, how can we satisfy the ASHRAE requirement for the maximum unmet load hours of 300hrs?
Ø Shall I add the hours underheated and hours undercooled of the SS-F report, or
Ø shall I add the "HOURS ANY ZONE ABOVE COOLING THROTTLING RANGE" and "HOURS ANY ZONE BELOW HEATING THROTTLING RANGE " hours of the BEPS report, or
Ø Shall I multiply the "% of hours any system zone outside of throttling range" of the BEPS report by the "hours fans on" of the SS-E report?
All the three above seem to give me different answers! Which one is the most accurate?
Many thanks!
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 266
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100922/5d562367/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100922/5d562367/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100922/5d562367/attachment-0001.jpeg>
More information about the Equest-users
mailing list