Bill/Peter:

 

I might be missing something, but this is the sort of equipment I think
of when someone says infrared heater:  
http://www.spaceray.com/1_infrared-tube-heaters.php

 

Commonly found in auto garages and open-air outdoor venues.

 

If you're asking about how to model gas/electric radiant heaters of this
sort in eQuest - I think you've got a definite challenge.  You could
play the custom-space-heat-source-scheduling game for hours on end...
but I would first suggest trying a unit heater (gas or electric as
appropriate) with a fan kW/CFM of zero or nearly-zero - see if that
works without errors.  

 

The way this equipment really works is interesting/tricky to us modelers
because it does not need to heat the space air to what we'd normally
call "comfortable" temperatures as the heat can hit your skin and warm
you up without heating the air around you.  You might account for this
by modifying the zone heating schedule (the target air temperature) to a
lower figure - though I'm not sure off the top of my head what would be
an appropriate figure - any suggestions?

 

~Nick

 

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Peter
Hillermann
Sent: Thursday, September 09, 2010 12:27 PM
To: 'BLafley'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Infrared Heaters

 

Bill,

 

I just read about the infrared heater. If you are using people and
equipment

to absorb heat and reradiate it, you have to rely on your schedules to
tap

into that calculation.

 

I am totally guessing because I have never tried to set renewable energy
to

a personal and equipment schedule. I'm sure it can be done however when
you

look at heat generation from people it can vary from 450 BTU to 2500 BTU
so

good luck. I would probably go to ASHRAE and look at the thermal comfort

data for process and heat generation of people and use the same numbers
they

have set to those processes. Look at the equipment you are using and see

what it does. Add it all together and subtract from total energy that
the

building is consuming.

 

Man that is complicated, best of luck to you my friend.

 

Thanks,

 

PETER HILLERMANN

 

peterh at westallarchitects.com

 

westall

architects

3404 pierce drive

chamblee, georgia 30341

 

o 770.458.4113

f  770.458.5352

c 678.898.2936

 

westallarchitects.com

 

 

 

 

 

-----Original Message-----

From: equest-users-bounces at lists.onebuilding.org

[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Peter

Hillermann

Sent: Thursday, September 09, 2010 12:42 PM

To: 'BLafley'; equest-users at lists.onebuilding.org

Subject: Re: [Equest-users] Infrared Heaters

 

Bill,

 

Do you have a chart that shows how much renewable energy the unit
consumes

and then uses to create heat? What you need to do is create the item in
2

parts. Its renewable component, which might be a solar collector and
then

you set up a radiant heater in the room either as baseboard or as your

system in that zone.The thing that I have noticed while modeling is
there

are 2 things you are looking at.. products in your building and how they

consume energy, by amount and efficiency. The second is what are you
doing

to replace the energy... renewable or are you pulling it from the grid.
The

model does not care where it comes from as long as when you use the

renewable it is as efficient as you say it is. I typically use PVWatt

calculator and do manual calculations because someone taught me that.
You

can also set up a collector in the utility&economics tab under
photovoltaic

modules. This is where you will need the solar information on your

collector.

 

The weather file needs to be correct because this is where it is pulling

your solar radiation data from watts/meter squared or watts/feet
squared.

 

Hope this helps. (Easier to do by hand)

 

Thanks,

 

PETER HILLERMANN

 

peterh at westallarchitects.com

 

westall

architects

3404 pierce drive

chamblee, georgia 30341

 

o 770.458.4113

f  770.458.5352

c 678.898.2936

 

westallarchitects.com

 

 

 

 

-----Original Message-----

From: equest-users-bounces at lists.onebuilding.org

[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of BLafley

Sent: Thursday, September 09, 2010 10:22 AM

To: equest-users at lists.onebuilding.org

Subject: [Equest-users] Infrared Heaters

 

Hello,

 

Does anyone have any experience modeling ceiling hung infrared heaters
in

eQuest?

 

Thanks,

--

Bill Lafley

Energy Analyst

Center for Ecological Technology (CET)

320 Riverside Drive - 1A Florence, MA 01062 blafley at cetonline.org

<mailto:blafley at cetonline.org> / 413-586-7350 ext. 222

413-695-2730 (cell) Visit www.cetonline.org <http://www.cetonline.org>

Support our work <https://www.merchantamerica.com/cet/echopay/index.php>

 

_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to

EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

 

_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to

EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

 

_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100909/39540641/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100909/39540641/attachment.jpeg>


More information about the Equest-users mailing list