[Equest-users] Reduction of window area in detail mode!

Nick Caton ncaton at smithboucher.com
Thu Sep 9 08:22:03 PDT 2010


Another option that may actually be quicker/easier, particularly if you
have many windows of varying dimensions, would be to do this manually
(outside of a parametric run):

 

1.       Navigate to the building shell tab

2.       Click any window in the component tree

3.       Highlight the entire column of "Height" (or "Width")

4.       Let go of your mouse, press Ctrl+c

5.       Open Excel

6.       Ctrl+v

7.       Make a formula in the adjacent column that multiplies the
dimension by the ratio you need to get total window area back to 40%

8.       Drag that formula down

9.       Flex your accounting muscles and hammer the results into the
column in eQuest - you can position the windows side-by-side if you have
enough screen real-estate, or print the excel file out on paper if the
column is huge or that's easier on your eyes.

 

Since some rounding is involved, if you wanted to check the math before
step #9, you could copy the other (height/width) dimension across from
eQuest into a new column, and use excel to multiply your new areas
across and sum them up.

 

~Nick

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mark
Nieman
Sent: Thursday, September 09, 2010 9:49 AM
To: Arunabha Sau; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Reduction of window area in detail mode!

 

I believe you could create a parametric run that redefines the window
heights, so that you end up with 40% glazing area. You would have to do
the math for what the final height would be, but I think that's the
quickest way to back into the baseline model (other baseline parameters
can be done this way also). For example:

 

 

Mark Nieman, PE, CEM | McKinstry | Sr. Energy Engineer 
d 206.832.8152 | m 206.510.4760 | f 206.832.8552 
FOR THE LIFE OF YOUR BUILDING 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Arunabha Sau
Sent: Wednesday, September 08, 2010 5:32 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Reduction of window area in detail mode!

 

Hi Folks!

 

 

I've got assigned in one project in eQuest which does not have LEED
baseline model and I've to create it.

They have already done the model for incentive from the local
gas&electric company which is very detailed and it's in 'Detail mode' in
eQuest.

For the LEED baseline, I need to create windows 40% of the wall area but
here in the model everything is according to the design (more than
40%windows)!

 

I don't want to go every single window and re-size them! 

Is there any shortcut way to reduce the window by multiplying 'the'
fraction (40%/current window percent)?

To be specific, I am looking for some help using "if...then...else..if"
or any other kind of function; that way may be just creating a single
global parameter the window area can be reduced in a very less tedious
way.

Is there any particular help-file to write parameter-codes in eQuest?

 

Hope you understand my question.

Thanks for your time.

 

 

 

Best,

Aru


This email is the property of McKinstry or one of its affiliates and may
contain confidential and/or privileged information. If you are not the
intended recipient or have received this e-mail in error please notify
the sender immediately and delete this e-mail. Any unauthorized copying,
disclosure or distribution of the material in this e-mail is strictly
forbidden.   --  

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100909/d11e8057/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100909/d11e8057/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 31342 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100909/d11e8057/attachment.png>


More information about the Equest-users mailing list