Tang, Kevin Kevin.Tang at owenscorning.com
Mon Sep 6 00:46:31 PDT 2010


Thanks Vikram and Carol,

After increase reheat delta T(default is 30F,increase to 45 or 50)  ,throttling range and even size ratio, it's back to normal, thanks for your help!

But I wonder why this happen after switch software version?

Kevin

________________________________
发件人: Carol Gardner [mailto:cmg750 at gmail.com]
发送时间: 2010年9月2日 22:37
收件人: Sami, Vikram
抄送: (equest-users at lists.onebuilding.org); Tang, Kevin
主题: Re: [Equest-users] "Insufficient heating warnings" in 3.64

It sounds like you need to specify a thermostat type of reverse action. I would also increase the throttling range to 6. Look in the documentation for a discussion regarding VAV, thermostats and throttling range or look in the archives.

Carol

On Thu, Sep 2, 2010 at 7:24 AM, Sami, Vikram <Vikram.Sami at perkinswill.com<mailto:Vikram.Sami at perkinswill.com>> wrote:
What is your reheat delta T?

Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462    f: 404.892.5823       e: vikram.sami at perkinswill.com<mailto:vikram.sami at perkinswill.com>   www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will.  Ideas + buildings that honor the broader goals of society


From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Tang, Kevin
Sent: Thursday, September 02, 2010 6:09 AM
To: (equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>)
Subject: [Equest-users] "Insufficient heating warnings" in 3.64


Dear all,

I have a LEED model, after switched the version into v3.64 from v3.63,  a lot of insufficient heating warnings like below are reported,  the percent of hours outside throttling range is also rise,   while the model has been adjusted to no warnings and within 300hours in v3.63,   it's a VAV system with electric cooling in summer and purchased heat in winter.

**WARNING**********************************************************************
             ZONE E21 North Perim Zn (G.N1)
             might have insufficient heating capability.
             Check that the SYSTEM or ZONE HEATING-CAPACITY plus this
             ZONEs BASEBOARD-RATING is adequate to maintain the ZONE
             specified DESIGN-HEAT-T for the calculated peak ZONE load
             (see LS-A or LS-B for the ZONE peak load.)

             ZONE E21 North Perim Zn (G.N1)        has a THERMOSTAT-TYPE
             of REVERSE-ACTION, which, when added to the issues listed
             in the messages above, will cause excessive underheating.

I noticed  both No.33 and No.46 in file Bugfixes-047h.pdf<http://doe2.com/download/DOE-22/Bugfixes-047h.pdf> mentioned there are enhancements for "insufficient heating capability" in V3.64, I tried increasing "heat sizing ratio" and "throttle range", but failed, can anyone give me some guidance to fix this issue ?   I wish can benefit from soem new features in v3.64, but  it's close to the end of project, there is little space to play.

Thanks in advance for your help!


Best Regards
Kevin Tang
Project Engineer | Energy Solution | Owens Corning China
Tel: 8621-6101 9622 | Fax 8621- 6101 9588
Kevin.tang at owenscorning.com<mailto:Kevin.tang at owenscorning.com>



The information contained in this communication and its attachment(s) is intended only for the use of the individual to whom it is addressed and
may contain information that is privileged, confidential, or exempt from disclosure. If the reader of this message is not the intended recipient,
you are hereby notified that any dissemination, distribution, or copying of this communication is strictly prohibited. If you have received this
communication in error, please notify postmaster at owenscorning.com<mailto:postmaster at owenscorning.com> and delete the communication without retaining any copies. Thank you.

Translations available: http://www.owenscorning.com/emailfooter.html

This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>




--
Carol Gardner PE

The information contained in this communication and its attachment(s) is intended only for the use of the individual to whom it is addressed and may contain information that is privileged, confidential, or exempt from disclosure. If the reader of this message is not the intended recipient, you are hereby notified that any dissemination, distribution, or copying of this communication is strictly prohibited. If you have received this communication in error, please notify postmaster at owenscorning.com and delete the communication without retaining any copies. Thank you. 

Translations available: http://www.owenscorning.com/emailfooter.html
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100906/07586aef/attachment.htm>


More information about the Equest-users mailing list