[Equest-users] Occupancy Sensors

Michael Mantai mmantai at systemworcx.com
Sat Oct 30 04:56:33 PDT 2010


Section 9.4.1.2 requires occupancy sensors in the following spaces:

1.classrooms (not including shop classrooms, laboratory classrooms, and
preschool through 12th grade class-rooms)
2.conference/meeting rooms
3.employee lunch and break rooms.

Any other areas that have occupancy sensors can be credited in the energy
model.


On 10/29/10 8:58 PM, "Rimes, Christie" <Christie.Rimes at wspfk.com> wrote:

> Hi,
>  
> I am a little confused as to what areas I can take claim for having occupancy
> sensors under ASHRAE 90.1 2007? I have looked at section 9.4.1 however it is
> not very clear. Any help would be greatly appreciated.
>  
> Cheers,
>  
> 
>  
> 
> 