It possible. Reheat can be a really large load - I've seen labs where 50% of the energy usage was reheat (in Summer).
In most labs, the hot labs control the supply air temperature and the ventilation driven labs end up using a LOT of reheat energy. Chilled beams are really a strategy to reduce reheat loads by allowing you to reset your supply air temperature.
A good sanity check is to submeter the reheat coils. This is easier to do if its electric or attached to a campus steam/hot water system. If it's a boiler I would create a separate boiler for the reheat coils (just for diagnosis).
You could attach your inp file too.
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com
Perkins+Will. Ideas + buildings that honor the broader goals of society
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Fred Betz
Sent: Thursday, October 28, 2010 4:49 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Large Heating Savings from Chilled Beams
All,
I am getting unusually high heating energy savings, ~50%, when I apply chilled beams (induction units) to patient rooms in a hospital.
I just stumbled across another energy report written by another firm for a laboratory project of ours that shows the same results, ~50% heating energy savings when applying chilled beams.
The cooling and electricity savings are in line with what would be considered reasonable and I realize there should be some heating savings due to a reduced reheat load, but 50% seems excessive.
Both buildings have approximately 40% of the floor area using chilled beams.
The lab is in a cold climate, the hospital is in a more temperate climate.
Has anyone else come across this issue?
Thanks,
Fred
FRED BETZ PhD., LEED AP
SUSTAINABLE SYSTEMS ANALYST
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI 53719
P: 608.236.1175 | F: 608.238.2614
fbetz at aeieng.com | www.aeieng.com
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
More information about the Equest-users
mailing list