[Equest-users] 90.1 Baseline HVAC System 7 - VAV w Reheat andBaseboard
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Oct 28 07:57:28 PDT 2010
Jonathan,
ASHRAE Standard 90.1-2007, Appendix G. section G3.1.2.4 requires fan
cycling to meet heating and cooling loads during unoccupied hours.
Appendix G. does not provide guidance on the use of baseboard heating.
My approach has been to always leave baseboards out of the baseline
building design.
There is a discussion on the Bldg-Sim list today about ventilation rates
per G3.1.2.5. There seem to be as many interpretations of this section
as there are energy modelers. In the case of a proposed fan system that
shuts off at night, I would model the baseline with a MIN-AIR-SCH, set
to 0 during unoccupied hours, so that no ventilation is provided during
nighttime fan cycling.
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - the forest AND the trees. P
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Jonathan Smith
Sent: Thursday, October 28, 2010 10:28 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] 90.1 Baseline HVAC System 7 - VAV w Reheat
andBaseboard
eQuesters:
To comply with 90.1-2007 System Type 7, do I need to have supplemental
heat with baseboards if I have it in the proposed system? Or, is it
allowable to meet nighttime heating demands by cycling fans during
unoccupied hours to meet nighttime setback temperature?
In the proposed model during unoccupied periods I have fans OFF with
baseboards providing supplemental heat.
Thanks in advance for your feedback.
Jonathan R. Smith AIA LEED(r)AP
40 Beaver Street
Albany, New York 12207
p: 518.463.8068 x268
f: 518.463.8069
www.csarchpc.com <http://www.csarchpc.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101028/3a03206c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11096 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101028/3a03206c/attachment.jpeg>
More information about the Equest-users
mailing list