[Equest-users] Non-vertical windows
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Wed Oct 27 19:39:42 PDT 2010
Yes, you can specify angled walls in DDedit mode. When you are in DDedit,
find the actual wall that you want to tilt, open the properties window and
you will find an input for the tilt angle. Be mindful that you will have
to make sure that all other surfaces adjacent to this angled surface are
then adjusted for their geometry so that all the constructions line up as
they should.
pkg
2010/10/27 Marie-Claude Hamelin <marie-claude.hamelin at usherbrooke.ca>
> Hi,
> I am trying to model a building which has a non-vertical structure; the
> walls and windows on the north and south sides are oriented to benefit as
> much as possible from the sun. Is there a way to model an angled wall, or at
> least the windows, for solar gains? Thanks!
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101027/a0fd1f36/attachment.htm>
More information about the Equest-users
mailing list