Thank you very much.

I got it now. You explained it quite well enough.

 

Syed

 

 

 

From: Fleming, Joe [mailto:joe.fleming at tlc-eng.com] 
Sent: Wednesday, October 27, 2010 11:46 AM
To: Syed Mohsin Abidi; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Seasonal Thermostat Set Point

 

>From Building Description Detailed Edit Mode, click on the Component Tree
tab in the bottom left next to Actions.  Scroll down to the Annual schedules
that you want to change and double click to open, (if you don't know which
schedule you need to revise you can click on the Thermal Zone, in the
Air-Side HVAC tab and locate the T-stat schedule in there).  If you have all
of your seasonal schedules in the annual schedule from the wizard, then you
can click on the Day Schedules tab and adjust your set-points as needed for
the given week schedule or "season".  If it is not broken down into seasons
then you will need to create a few more week and day schedules  and add them
to your annual schedule "weekly schedule assignments".  You can right click
on a day or week schedule to create a new one.  You want to create a
schedule type "temperature".  After you have created all of the schedules
you want, assign them to the proper season by inserting week in the annual
schedules tab and choosing the proper week schedule.  Make sure to assign
the proper days and set-points in the week schedules tab.

 

Joe Fleming

E.I., LEED AP BD+C, BEMP

Mechanical Engineer I

 

TLC Engineering for Architecture
Your 2030 Challenge Partner

 

800 Fairway Drive, Suite 250

Deerfield Beach, FL 33441-1816

 


phone: 

954-418-9096


fax: 

954-418-9296


direct: 

954-418-4591


website: 

www.tlc-engineers.com

 

 <http://www.tlc-engineers.com/>
http://www.tlc-engineers.com/images/TLC_Sig_Loc_Block.gif

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Syed Mohsin
Abidi
Sent: Wednesday, October 27, 2010 10:01 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Seasonal Thermostat Set Point

 

How to change the seasonal thermostat set points for heating and cooling in
detailed data edit mode?

I forgot to change it in the wizard mode.

Please guide.

 

Syed M. Abidi, EIT, LEED AP

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101027/0237a34b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 5272 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101027/0237a34b/attachment.gif>


More information about the Equest-users mailing list