[Equest-users] VRV Special case: is it worth modeling?
Berke Çelikel
berkecelikel at erketasarim.com
Sun Oct 24 23:23:41 PDT 2010
I agree with Gary I have never see that high COP for the VRV units. It can
be EER value. Please check that value again to avoid any mistake.
Good luck
Yük.Müh.Berke Çelikel
Lis.Mak.Müh/Yük.Lis.End.Müh.(Müh.Yön.)
BSc.Mech. Eng./MSc.Ind.Eng.(Eng. Man.)
From: Gary.Schrader at buildings.schneider-electric.com
[mailto:Gary.Schrader at buildings.schneider-electric.com]
Sent: Thursday, October 14, 2010 6:11 PM
To: omar at ecoconsulting.net; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] VRV Special case: is it worth modeling?
Omar,
The only thing that would save you a significant amount of energy in my
opinion would have been scheduling large VAV air handling and plant
equipment that was originally serving them. I had a project where I took
data closets off of the VAV units and put VRV units in the closets so that
the VAV units no longer had to run 24/7. Scheduling these large VAV units
had a significant savings impact.
In your case, it sounds like you may have something similar but I would need
clarification. You said that your closets (that you want to convert to VRV)
are currently FCU. I assume that these FCUs are served by chilled water. By
switching these closets over to VRV, are you able to now schedule the
chiller off? If yes, I would assume that significant savings would result by
not running a chiller (and pumping) 24/7, even with a high unloading
capability and variable-speed pumping. (If you had low unloading capability
and constant pumping, more savings would result)
At face value, simply changing the efficiency of the cooling equipment isn't
enough to evaluate energy savings. If, however, you can significantly change
the schedule of plant equipment because it is isolated from zones that
require 24/7 operation, savings could be significant and I would certainly
recommend a model.
Sidenote: 10 COP seems very, very high for even the best VRV equipment. I
would check that value to ensure accuracy.
Best luck,
Gary
____________________________________________________________________________
___________________________________________
Gary Schrader | Schneider Electric | Buildings Business | Energy Solutions |
Engineer I
Phone: +1 913 217 8068 | Fax: +1 913 469 0206
Email: gary.schrader at buildings.schneider-electric.com | Site:
www.schneider-electric.com/buildings | Address: 16011 College Boulevard,
Suite 212, Lenexa, KS 66219, USA
*** Please consider the environment before printing this email.
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar
Katanani
Sent: Thursday, October 14, 2010 5:41 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] VRV Special case: is it worth modeling?
Dear all,
My school has some 200 zones including classrooms, storage rooms, offices...
The HVAC system is a VAV one, with FCU for 17 offices/storage rooms.
In the new updated design, 4 of these FCUs were replaced with a VRV system.
I am about to model that:
Do you think that these 4 small zones (electrical room (x 2), UPS room,
telephone room) will significantly change the Space Cooling results (not
that no heating is required)? I mean, these zones had FCUs and were
conditioned. All that changed is that a VRV (COP=10) replaced the chiller
(COP=5.4) for only 4 zones!
I would like to avoid the complexity of modeling VRVs if possible!
Many thanks,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 266
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101025/02740797/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101025/02740797/attachment.jpeg>
More information about the Equest-users
mailing list