[Equest-users] DOAS results
Brian Fountain
bfountain at greensim.com
Wed Oct 20 09:22:44 PDT 2010
Remember that eQUEST doesn't /really/ do DOAS yet. All it does is set
the OA temperature for the borrowing zone using the OA-FROM keyword to
the RA temperature of the "lending" system (which is why it has to come
first on the system list).
I really hope this changes in future releases!
On 10/19/2010 7:25 PM, Carol Gardner wrote:
> Are you willing to share your .inp and .pd2 input decks? I would take
> a quick look if you are.
>
> Carol
>
> On Tue, Oct 19, 2010 at 12:40 PM, Fleming, Joe
> <joe.fleming at tlc-eng.com <mailto:joe.fleming at tlc-eng.com>> wrote:
>
> I know this topic has been beaten like..., but the results I have
> been getting for the ## hours on a model with several DOAS's are
> horrible, (getting a little delirious at this point). There is a
> DOAS for each system with a different schedule than the next.
> Each DOAS has an ERV which operates with a DH of 2.0btuh/hr in
> cool/heat and float.
>
> I feel like the problem is within the dummy zone or the schedules.
>
> When I assign the DOAS air to the SZRH unit as OA from System the
> cooling load shoots up by about 50%, (even when I remove the ERV
> the results are similar, increased cooling).
>
> The building is in a moderate climate zone.
>
> The DOAS fan schedule is set to on at the same time as the SZRH unit.
>
> The heating energy is reduced when I assign the DOAS.
>
> The problems I see are, to list a few;
>
> The dummy zone has all of its hours outside of the throttling
> range no matter how it is assigned and no matter what the t-stat
> schedule I assign.
>
> The load doesn't budge once I remove the DOAS from the model, only
> when I add it to the SZRH unit as OA from system.
>
> The DOAS does not show any heating load, only cooling load all
> year long (again moderate climate with cold seasons).
>
> DOAS's have been done before without this problem, maybe adding
> too much info this time.
>
> _*How is the DOAS operating in eQuest?_
>
> Taking a stab I assume it is bringing in the OA and cooling it or
> heating it to whatever the temperature set-points are. Depending
> on the schedules the temp could be floating most of the time. The
> air is then brought into your secondary system at set-point or
> floating point. The OA from the zones attached to the secondary
> system are replaced by the OA from the DOAS. (?) Then the
> secondary system does its thing as usual.
>
> (Not sure what is happening with the dummy zone? Does DZ care it
> gets any air? Looks like it does because of the unmet hours.
> Does the secondary system pick up the air from the DOAS after it
> has traveled through a space and picked up load? The dummy zone
> has no load but it's temp is always above 85.)
>
> Now for the cooling to be increasing, the air must be coming in to
> the secondary system warmer than usual during cooling hours.
> (usual being the raw temperature of uncond outdoor air). But
> the results seem extreme.
>
> For the heating to be decreasing the air must be coming in warmer
> than usual for the secondary system, which it is based on SS-O.
>
> Does anyone have experience with this and what could be going wrong?
>
> _*Or, can someone link me to a basic DOAS goby? _
>
> I have searched the archives but many of the DOAS questions have
> gone unanswered in the past.
>
> Thank You
>
> *Joe Fleming*
>
> /E.I., LEED AP BD+C, BEMP/
>
> /Mechanical Engineer I/
>
> *TLC Engineering for Architecture
> **Your 2030 Challenge Partner***
>
> 800 Fairway Drive, Suite 250
>
> Deerfield Beach, FL 33441-1816
>
> phone:
>
>
>
> 954-418-9096
>
> fax:
>
>
>
> 954-418-9296
>
> direct:
>
>
>
> 954-418-4591
>
> website:
>
>
>
> www.tlc-engineers.com <http://www.tlc-engineers.com>
>
> http://www.tlc-engineers.com/images/TLC_Sig_Loc_Block.gif
> <http://www.tlc-engineers.com/>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> --
> Carol Gardner PE
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com
> Version: 9.0.862 / Virus Database: 271.1.1/3206 - Release Date: 10/19/10 02:34:00
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101020/e602179e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 5272 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101020/e602179e/attachment.gif>
More information about the Equest-users
mailing list