[Equest-users] DOAS results

Fleming, Joe joe.fleming at tlc-eng.com
Tue Oct 19 12:40:12 PDT 2010


I know this topic has been beaten like..., but the results I have been getting for the ## hours on a model with several DOAS's are horrible, (getting a little delirious at this point).  There is a DOAS for each system with a different schedule than the next.  Each DOAS has an ERV which operates with a DH of 2.0btuh/hr in cool/heat and float.
I feel like the problem is within the dummy zone or the schedules.
When I assign the DOAS air to the SZRH unit as OA from System the cooling load shoots up by about 50%, (even when I remove the ERV the results are similar, increased cooling).
The building is in a moderate climate zone.
The DOAS fan schedule is set to on at the same time as the SZRH unit.
The heating energy is reduced when I assign the DOAS.

The problems I see are, to list a few;
The dummy zone has all of its hours outside of the throttling range no matter how it is assigned and no matter what the t-stat schedule I assign.
The load doesn't budge once I remove the DOAS from the model, only when I add it to the SZRH unit as OA from system.
The DOAS does not show any heating load, only cooling load all year long (again moderate climate with cold seasons).
DOAS's have been done before without this problem, maybe adding too much info this time.


*How is the DOAS operating in eQuest?
Taking a stab I assume it is bringing in the OA and cooling it or heating it to whatever the temperature set-points are.  Depending on the schedules the temp could be floating most of the time.  The air is then brought into your secondary system at set-point or floating point.  The OA from the zones attached to the secondary system are replaced by the OA from the DOAS. (?)  Then the secondary system does its thing as usual.
(Not sure what is happening with the dummy zone?  Does DZ care it gets any air?  Looks like it does because of the unmet hours.  Does the secondary system pick up the air from the DOAS after it has traveled through a space and picked up load?  The dummy zone has no load but it's temp is always above 85.)

Now for the cooling to be increasing, the air must be coming in to the secondary system warmer than usual during cooling hours.  (usual being the raw temperature of uncond outdoor air).   But the results seem extreme.
For the heating to be decreasing the air must be coming in warmer than usual for the secondary system, which it is based on SS-O.

Does anyone have experience with this and what could be going wrong?
*Or, can someone link me to a basic DOAS goby?
I have searched the archives but many of the DOAS questions have gone unanswered in the past.

Thank You

Joe Fleming
E.I., LEED AP BD+C, BEMP
Mechanical Engineer I

TLC Engineering for Architecture
Your 2030 Challenge Partner

800 Fairway Drive, Suite 250
Deerfield Beach, FL 33441-1816

phone:

954-418-9096

fax:

954-418-9296

direct:

954-418-4591

website:

www.tlc-engineers.com<http://www.tlc-engineers.com>


[cid:image001.gif at 01CB6F9F.77B8BCF0]<http://www.tlc-engineers.com/>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/27156c54/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 5272 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/27156c54/attachment.gif>


More information about the Equest-users mailing list