[Equest-users] F-Factor to U-Value
Brian Fountain
bfountain at greensim.com
Thu Oct 14 10:08:36 PDT 2010
Attached please find the research paper that eQUEST Wizards (and EE4
for you Canucks) use as a basis to convert F-factor to U-factor for a
variety of foundation wall insulation configurations.
On 10/14/2010 12:24 PM, Nick Caton wrote:
> F-factors can't be entered directly, but are still pretty easy to handle in eQuest.
>
>
>
> Open your copy of 90.1, and add a tab to Table A6.3, and read preceding section A6.
>
>
>
> 90.1 is explicit in what physically constitutes a floor slab with a given F-factor. Typically, I need an unheated slab with F-0.73. From this table and accompanying text I know that means simply to define a 6in. thick slab on grade with zero insulation while in the wizards. eQuest does the rest.
>
>
>
> I generally utilize the default library material properties (mass/conductivity) built into eQuest. Those properties came under fire once from a nitpicky reviewer for being slightly different from Appendix A's final tables (see archives), but I learned after-the-fact that the material properties listed in 90.1 are derived from DOE2's libraries, so it was a moot issue.
>
>
>
> ~Nick
>
>
>
>
>
>
>
> NICK CATON, E.I.T.
>
> PROJECT ENGINEER
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> Check out our new web-site @ www.smithboucher.com
>
>
>
> From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Will Mak
> Sent: Thursday, October 14, 2010 10:47 AM
> To: equest-users at lists.onebuilding.org
> Subject: Re: [Equest-users] F-Factor to U-Value
>
>
>
> eQuest requires an input of a U-Value when modeling a slab on grab layer. Typically, you enter a F-Factor to account for the loss per perimeter length. I did some research but could not find any solid conclusions on what is suppose to be done to convert the F-Factor to a U-value or configure eQuest to correctly model this. Any suggestions?
>
>
>
> Thanks!
>
>
>
> William Mak, LEED Green Associate
> Mechanical Design Engineer
>
> EPSTEIN
> Architecture
> Interiors
> Engineering
> Construction
>
> 600 West Fulton Street
> Chicago, Illinois 60661-1259
>
> D (312) 429-8116
> F (312) 559-1217
> wmak at epsteinglobal.com<mailto:hmoats at epsteinglobal.com>
> www.epsteinglobal.com<http://www.epsteinglobal.com/>
>
> þ Epstein is a firm believer in sustainability. We ask that you please consider the environment before printing this e-mail.
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com
> Version: 9.0.862 / Virus Database: 271.1.1/3196 - Release Date: 10/14/10 02:34:00
>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: UnderGroundSurfaces in DOE2.pdf
Type: application/pdf
Size: 65922 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101014/a32c4c26/attachment.pdf>
More information about the Equest-users
mailing list